Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default Electrical Dimming

We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring. Over the years we have a consistent problem with a
kitchen light in the middle of the ceiling browning out after we turn
it on. It turns on just fine and a few seconds later it dims and then
goes back to full light. It might never do it again or it might repeat
this. We've been unable to establish a pattern.

We've been all over the house and exterior trying to tie that
particular behavior with appliances turning on or off, the washer
changing cycles or something and can't. We've had three separate
electricians try to diagnose and fix the problem but they keep trying
to say that it's a general brownout of the neighborhood when it clearly
is not.

We've changed the switches in the kitchen and elsewhere and "pigtailed"
the switches. I'm imagining that if there were a danger of fire we
would have had one by now so I'm assuming this is not a clearly unsafe
condition. One neighbor suggested that if there one non-aluminum line
on a circuit that this might be the source. Someone had added some
wiring before we bought the house. Does this make any sense or can you
suggest another direction to look?

  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical Dimming


bardsapprentice wrote:
We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring. Over the years we have a consistent problem with a
kitchen light in the middle of the ceiling browning out after we turn
it on. It turns on just fine and a few seconds later it dims and then
goes back to full light. It might never do it again or it might repeat
this. We've been unable to establish a pattern.

....

can you suggest another direction to look?


Well, if other outlets/lights on the circuit are not affected, and
switches/connections to the fixture in question didn't resolve it, it's
isolated to either the fixture itself or in the wiring itself between
the fixture/switch. I'd start by looking a the connections to the
fixture and then suspect the base of the fixture -- bases will oxidize
or the base spring relax, etc.

I wouldn't assume because you haven't had a fire yet you
wouldn't/won't.

My inclination would be to simply replace the fixture if it's just an
ordinary ceiling fixture. If you have a spare or an accessible
porcelin bulb base somewhere, substitute it for a few days and see if
the problem doesn't go away...

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 44
Default Electrical Dimming

Sounds like a loose connection - but where? The first place I would
check is the circuit breaker. Aluminum wiring is well-known as a fire
hazard because it's such a good conductor of heat and it expands and
contracts so much (compared to copper) that terminations eventually
loosen over time and get warm as they do (because of resistance) and as
they warm, they expand and then contract when the switch is turned off.
Every time the switch cycles (gets turned on and off) the wire warms
and cools further loosening the connection until you start having the
"brown out" condition you describe. Sometimes there will be an arc in
the loose joint and the condition will disappear for a while (the wire
actually welds itself) until the heat/cooling cycle builds up enough to
break the little weld and you're back to the brown out condition.

Somewhere between the circuit breaker box and your fixture there is a
loose connection and I would consider it VERY unsafe and a potential
fire hazard. Find a different electrician. No self-respecting
electrician would EVER leave a homeowner with the described condition,
furthermore if that electrician wants to keep working and avoid having
the liability of a fire (and all the consequences that can accompiany
that) on his record.

Jeff



bardsapprentice wrote:
We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring. Over the years we have a consistent problem with a
kitchen light in the middle of the ceiling browning out after we turn
it on. It turns on just fine and a few seconds later it dims and then
goes back to full light. It might never do it again or it might repeat
this. We've been unable to establish a pattern.

We've been all over the house and exterior trying to tie that
particular behavior with appliances turning on or off, the washer
changing cycles or something and can't. We've had three separate
electricians try to diagnose and fix the problem but they keep trying
to say that it's a general brownout of the neighborhood when it clearly
is not.

We've changed the switches in the kitchen and elsewhere and "pigtailed"
the switches. I'm imagining that if there were a danger of fire we
would have had one by now so I'm assuming this is not a clearly unsafe
condition. One neighbor suggested that if there one non-aluminum line
on a circuit that this might be the source. Someone had added some
wiring before we bought the house. Does this make any sense or can you
suggest another direction to look?


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Electrical Dimming


"dpb" wrote in message
oups.com...

bardsapprentice wrote:
We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring. Over the years we have a consistent problem with a
kitchen light in the middle of the ceiling browning out after we turn
it on. It turns on just fine and a few seconds later it dims and then
goes back to full light. It might never do it again or it might repeat
this. We've been unable to establish a pattern.

...

can you suggest another direction to look?


Well, if other outlets/lights on the circuit are not affected, and
switches/connections to the fixture in question didn't resolve it, it's
isolated to either the fixture itself or in the wiring itself between
the fixture/switch. I'd start by looking a the connections to the
fixture and then suspect the base of the fixture -- bases will oxidize
or the base spring relax, etc.

I wouldn't assume because you haven't had a fire yet you
wouldn't/won't.

My inclination would be to simply replace the fixture if it's just an
ordinary ceiling fixture. If you have a spare or an accessible
porcelin bulb base somewhere, substitute it for a few days and see if
the problem doesn't go away...


I concur. Remove the light fixture and put a pigtail socket and bulb there
for a few days and see what happens. I recently installed an expensive
Italian design light fixture for a customer. While I was there some of the
bulbs would go out and come back on a short time later. I tightened the
bulbs which seemed to help, but the problem would not go away. Inside the
small lamp sockets was a narrow strip of metal on the side that was suppose
to come in contact with the shell of the bulb. I bent the strips forward a
little on each socket and the problem went away.

  #5   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical Dimming


jeffreydesign wrote:
Sounds like a loose connection - but where? The first place I would
check is the circuit breaker....
Somewhere between the circuit breaker box and your fixture there is a
loose connection and I would consider it VERY unsafe and a potential
fire hazard. ...


Given that the symptom appears to occur only in one fixture, it would
appear localized well beyond the circuit breaker...as I noted in
another response, I would venture most likely is the fixture base
itself, then the connection _to_ the fixture, then internal in the
fixture...after eliminating those possibilities I'd start casting a
wider net...

I don't disagree it is a potential hazard...

... Find a different electrician. No self-respecting
electrician would EVER leave a homeowner with the described condition,
furthermore if that electrician wants to keep working and avoid having
the liability of a fire (and all the consequences that can accompiany
that) on his record.

.....

Well, they say they've tried three already...agree it would seem they
should have been able to isolate something, but this is a little
over-the-top on liability -- if they didn't do anything, there's little
they can be liable for imo. Inability to find/solve a problem not of
their creating isn't an offense that I'm aware of...



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 831
Default Electrical Dimming


bardsapprentice wrote:
We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring.

snip
We've changed the switches in the kitchen and elsewhere and "pigtailed"
the switches.


I hope you didn't pigtail with purple wirenuts
http://www.inspect-ny.com/aluminum/ideal65.htm

This device seems better and is only slighty larger than a 'red'
wirenut
http://www.kinginnovation.com/products/alumiconn.html
I have no ties to King just passing on a _potentially_ better product.
There are also special switches and outlets that are designed for use
with aluminum wiring.

I agree with most of what has been said. If you are comfortable I
would pull the panel cover and check the tightness of the connections
in your breaker box. I also have aluminum wiring and tightened all of
the screws and less than a year later at least three were loose.

Lights will give you an immediate indication of a problem on a circuit
because it is visual. A toaster on the same circuit will give you no
indication of the same problem.

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 60
Default Electrical Dimming

Had a similar problem once but had all copper wire. Power company found a
loose connection at the transformer.
"RayV" wrote in message
ups.com...

bardsapprentice wrote:
We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring.

snip
We've changed the switches in the kitchen and elsewhere and "pigtailed"
the switches.


I hope you didn't pigtail with purple wirenuts
http://www.inspect-ny.com/aluminum/ideal65.htm

This device seems better and is only slighty larger than a 'red'
wirenut
http://www.kinginnovation.com/products/alumiconn.html
I have no ties to King just passing on a _potentially_ better product.
There are also special switches and outlets that are designed for use
with aluminum wiring.

I agree with most of what has been said. If you are comfortable I
would pull the panel cover and check the tightness of the connections
in your breaker box. I also have aluminum wiring and tightened all of
the screws and less than a year later at least three were loose.

Lights will give you an immediate indication of a problem on a circuit
because it is visual. A toaster on the same circuit will give you no
indication of the same problem.



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 229
Default Electrical Dimming

It's down to two likely problems. A poor connection to that lamp
somewhere or a floating neutral. Both can be serious and the fact that you
home has not burned down yet is not evidence of no problems, in fact you
have a known problem and maybe others unknown.

I know you will not like this advice and there will be some who will say
I am being over concerned, but if it were my home I would have a qualified
electriction go over the whole home and verify that it is all in good shape,
not just that light. If not, make sure the batteries are changed in your
smoke detectors!

--
Joseph E. Meehan




"bardsapprentice" wrote in message
oups.com...
We've lived in a home for 20 years that was built in 1970. It has
aluminum wiring. Over the years we have a consistent problem with a
kitchen light in the middle of the ceiling browning out after we turn
it on. It turns on just fine and a few seconds later it dims and then
goes back to full light. It might never do it again or it might repeat
this. We've been unable to establish a pattern.

We've been all over the house and exterior trying to tie that
particular behavior with appliances turning on or off, the washer
changing cycles or something and can't. We've had three separate
electricians try to diagnose and fix the problem but they keep trying
to say that it's a general brownout of the neighborhood when it clearly
is not.

We've changed the switches in the kitchen and elsewhere and "pigtailed"
the switches. I'm imagining that if there were a danger of fire we
would have had one by now so I'm assuming this is not a clearly unsafe
condition. One neighbor suggested that if there one non-aluminum line
on a circuit that this might be the source. Someone had added some
wiring before we bought the house. Does this make any sense or can you
suggest another direction to look?



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home electrical problem thomas rush Electronics Repair 7 November 22nd 05 03:31 AM
Do they make white electrical tape? Harry Everhart Home Repair 6 June 16th 05 06:02 AM
Easiest way to ground a computer? Julie P. Home Repair 66 May 11th 05 06:10 PM
Installing Electrical Outlet In Sink Cabinet Matty Home Repair 0 August 27th 03 03:08 PM
Installing Ceiling Fan with Red wire on electrical box. Josh Home Repair 20 July 31st 03 11:53 AM


All times are GMT +1. The time now is 06:00 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"