AC question, what's the little circuit board in the compressor
cabinet?

My friend's AC is a Lennox HS26-311-1P. Its in-house fan goes on, but
the air isn't cooled, and the thing outside makes no noise and the fan
doesn't spin. (It worked fine all summer and just broke a couple
weeks ago, he happily reports.)

The thermostat is calling for cooling, and the wires from the furnace
where they come into the compressor cabinet have 24 volts across them.

Moving along the wires to their destinations, I find the same 24 volts
between a black wire at one terminal of the contactor and a black wire
at one terminal of a little circuit board next to the contactor. But
the contactor hasn't closed the circuit.

The board is 2 inches by 2 inches or less and has 3 terminals, in,
out, and ground, or maybe common (I forget). It has a few each of
diodes, resistors, transistors and a shiny black almost cube, less
than 1x1x1 inch, which I think might be a relay.

What is the purpose of this board, and what is it called??

When I push in the plastic thing in the middle of the contactor, the
compressor goes on and sounds fine. That's not proof yet that the
problem is the contactor, is it??

I couldn't figure out the diagram inside the cover, or the manual. For
example, it didn't have the circuit board afaict. I think I have to
make my own diagram, and find out what is the second terminal for the
primary of the contactor. Is it the small black wire on the same
side, right next to the other black wire that I've already
identified??

A new contactor is about 130 dollars. This one is 11 years old but
looks like new. I think if it is broken the odds are 50/50 I can
repair it. Should I try??

Thanks



  #2   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default AC question, what's the circuit board in the compressor cabinet?

mm wrote:

AC question, what's the little circuit board in the compressor
cabinet?

My friend's AC is a Lennox HS26-311-1P. Its in-house fan goes on, but
the air isn't cooled, and the thing outside makes no noise and the fan
doesn't spin. (It worked fine all summer and just broke a couple
weeks ago, he happily reports.)

The thermostat is calling for cooling, and the wires from the furnace
where they come into the compressor cabinet have 24 volts across them.

Moving along the wires to their destinations, I find the same 24 volts
between a black wire at one terminal of the contactor and a black wire
at one terminal of a little circuit board next to the contactor. But
the contactor hasn't closed the circuit.

The board is 2 inches by 2 inches or less and has 3 terminals, in,
out, and ground, or maybe common (I forget). It has a few each of
diodes, resistors, transistors and a shiny black almost cube, less
than 1x1x1 inch, which I think might be a relay.

What is the purpose of this board, and what is it called??

When I push in the plastic thing in the middle of the contactor, the
compressor goes on and sounds fine. That's not proof yet that the
problem is the contactor, is it??

I couldn't figure out the diagram inside the cover, or the manual. For
example, it didn't have the circuit board afaict. I think I have to
make my own diagram, and find out what is the second terminal for the
primary of the contactor. Is it the small black wire on the same
side, right next to the other black wire that I've already
identified??

A new contactor is about 130 dollars. This one is 11 years old but
looks like new. I think if it is broken the odds are 50/50 I can
repair it. Should I try??

Thanks



Perhaps it's a timer to prevent short-cycling.

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,392
Default AC question, what's the circuit board in the compressor cabinet?

mm writes:

A new contactor is about 130 dollars.


Nope. About $20 on grainger.com.

Your description sounds like you have a short-cycle delay timer. You can
bypass it to diagnose that component vs the contactor.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default AC question, what's the circuit board in the compressor cabinet?

The board is a delay timer. So that the pressures in the system have
time to equalize before the compressor comes back on.

Sounds like you're over your head, here. Might be time to call an AC
service guy.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"mm" wrote in message
...
AC question, what's the little circuit board in the compressor
cabinet?

My friend's AC is a Lennox HS26-311-1P. Its in-house fan goes on, but
the air isn't cooled, and the thing outside makes no noise and the fan
doesn't spin. (It worked fine all summer and just broke a couple
weeks ago, he happily reports.)

The thermostat is calling for cooling, and the wires from the furnace
where they come into the compressor cabinet have 24 volts across them.

Moving along the wires to their destinations, I find the same 24 volts
between a black wire at one terminal of the contactor and a black wire
at one terminal of a little circuit board next to the contactor. But
the contactor hasn't closed the circuit.

The board is 2 inches by 2 inches or less and has 3 terminals, in,
out, and ground, or maybe common (I forget). It has a few each of
diodes, resistors, transistors and a shiny black almost cube, less
than 1x1x1 inch, which I think might be a relay.

What is the purpose of this board, and what is it called??

When I push in the plastic thing in the middle of the contactor, the
compressor goes on and sounds fine. That's not proof yet that the
problem is the contactor, is it??

I couldn't figure out the diagram inside the cover, or the manual. For
example, it didn't have the circuit board afaict. I think I have to
make my own diagram, and find out what is the second terminal for the
primary of the contactor. Is it the small black wire on the same
side, right next to the other black wire that I've already
identified??

A new contactor is about 130 dollars. This one is 11 years old but
looks like new. I think if it is broken the odds are 50/50 I can
repair it. Should I try??

Thanks




  #5   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default AC question, what's the circuit board in the compressor cabinet?

On Sun, 17 Sep 2006 20:22:42 -0500, Richard J Kinch
wrote:

mm writes:

A new contactor is about 130 dollars.


Nope. About $20 on grainger.com.


Wow. I thought 130 was a lot.

Your description sounds like you have a short-cycle delay timer. You can
bypass it to diagnose that component vs the contactor.


To give myself a pat on the back, I thought of that too, but wasn't at
all sure. I'm in pretty good shape now, but I won't work on it again
until next Sunday.


  #6   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default AC question, what's the circuit board in the compressor cabinet?

On Mon, 18 Sep 2006 02:25:37 GMT, "Stormin Mormon"
wrote:

The board is a delay timer. So that the pressures in the system have
time to equalize before the compressor comes back on.

Sounds like you're over your head, here. Might be time to call an AC
service guy.


Well, I was in over my head, but you answered my question for me!
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 286
Default AC question, what's the circuit board in the compressor cabinet?

check to see if the contactor has voltage across the coil, if it does,
then it's the contactor. otherwise it's you little mystery board.

Empressess #124457


The best Games


a href=http://www.gamestotal.com/Multiplayer Online Games/a a
href=http://www.gamestotal.com/Strategy Games/abra
href=http://uc.gamestotal.com/Unification Wars/a - a
href=http://uc.gamestotal.com/Massive Multiplayer Online
Games/abra href=http://gc.gamestotal.com/Galactic Conquest/a -
a href=http://gc.gamestotal.com/Strategy Games/abra
href=http://www.stephenyong.com/runescape.htmRunescape/abra
href=http://www.stephenyong.com/kingsofchaos.htmKings of chaos/abr





mm wrote:
AC question, what's the little circuit board in the compressor
cabinet?

My friend's AC is a Lennox HS26-311-1P. Its in-house fan goes on, but
the air isn't cooled, and the thing outside makes no noise and the fan
doesn't spin. (It worked fine all summer and just broke a couple
weeks ago, he happily reports.)

The thermostat is calling for cooling, and the wires from the furnace
where they come into the compressor cabinet have 24 volts across them.

Moving along the wires to their destinations, I find the same 24 volts
between a black wire at one terminal of the contactor and a black wire
at one terminal of a little circuit board next to the contactor. But
the contactor hasn't closed the circuit.

The board is 2 inches by 2 inches or less and has 3 terminals, in,
out, and ground, or maybe common (I forget). It has a few each of
diodes, resistors, transistors and a shiny black almost cube, less
than 1x1x1 inch, which I think might be a relay.

What is the purpose of this board, and what is it called??

When I push in the plastic thing in the middle of the contactor, the
compressor goes on and sounds fine. That's not proof yet that the
problem is the contactor, is it??

I couldn't figure out the diagram inside the cover, or the manual. For
example, it didn't have the circuit board afaict. I think I have to
make my own diagram, and find out what is the second terminal for the
primary of the contactor. Is it the small black wire on the same
side, right next to the other black wire that I've already
identified??

A new contactor is about 130 dollars. This one is 11 years old but
looks like new. I think if it is broken the odds are 50/50 I can
repair it. Should I try??

Thanks


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default AC question, what's the circuit board in the compressor cabinet?

However, a couple questions you didn't ask, and I didn't answer.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"mm" wrote in message
...
On Mon, 18 Sep 2006 02:25:37 GMT, "Stormin Mormon"
wrote:

The board is a delay timer. So that the pressures in the system have
time to equalize before the compressor comes back on.

Sounds like you're over your head, here. Might be time to call an AC
service guy.


Well, I was in over my head, but you answered my question for me!


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 114
Default AC question, what's the circuit board in the compressor cabinet?


"Stormin Mormon" wrote in message
...
However, a couple questions you didn't ask, and I didn't answer.


Like "Why is the storming Moron such an idiot?"


Christopher A. Young
You can't shout down a troll.
You have to starve them.
.

"mm" wrote in message
...
On Mon, 18 Sep 2006 02:25:37 GMT, "Stormin Mormon"
wrote:

The board is a delay timer. So that the pressures in the system have
time to equalize before the compressor comes back on.

Sounds like you're over your head, here. Might be time to call an AC
service guy.


Well, I was in over my head, but you answered my question for me!




  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default AC question, what's the circuit board in the compressor cabinet?

Stormin Mormon posted for all of us...

Sounds like you're over your head, here. Might be time to call an AC
service guy.

Which would NOT be Chris Young alias Stumped Moron
--
Tekkie "There's no such thing as a tool I don't need."


  #11   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default AC question, what's the circuit board in the compressor cabinet?

On 18 Sep 2006 03:24:19 -0700, wrote:

check to see if the contactor has voltage across the coil, if it does,
then it's the contactor. otherwise it's your little mystery board.


I think this summarizes the point I would have gotten to some time
this Sunday.

Thanks everyone.

BTW, as long as the amperage is adequate, do contactors have to be
made for a particular brand/model of AC?

I remember that I stripped one from a junked compressor unit this
year. I found it in the basement and it is 80 or 90% as big
physically as my fiend's and looking at it now, it looks brand new and
has about the same arrangement as the one my friend had. It has a 24
volts coil of course. I'm going to try to find its part number on the
web,





Empressess #124457


mm wrote:
AC question, what's the little circuit board in the compressor
cabinet?

My friend's AC is a Lennox HS26-311-1P. Its in-house fan goes on, but
the air isn't cooled, and the thing outside makes no noise and the fan
doesn't spin. (It worked fine all summer and just broke a couple
weeks ago, he happily reports.)

The thermostat is calling for cooling, and the wires from the furnace
where they come into the compressor cabinet have 24 volts across them.

Moving along the wires to their destinations, I find the same 24 volts
between a black wire at one terminal of the contactor and a black wire
at one terminal of a little circuit board next to the contactor. But
the contactor hasn't closed the circuit.

The board is 2 inches by 2 inches or less and has 3 terminals, in,
out, and ground, or maybe common (I forget). It has a few each of
diodes, resistors, transistors and a shiny black almost cube, less
than 1x1x1 inch, which I think might be a relay.

What is the purpose of this board, and what is it called??

When I push in the plastic thing in the middle of the contactor, the
compressor goes on and sounds fine. That's not proof yet that the
problem is the contactor, is it??

I couldn't figure out the diagram inside the cover, or the manual. For
example, it didn't have the circuit board afaict. I think I have to
make my own diagram, and find out what is the second terminal for the
primary of the contactor. Is it the small black wire on the same
side, right next to the other black wire that I've already
identified??

A new contactor is about 130 dollars. This one is 11 years old but
looks like new. I think if it is broken the odds are 50/50 I can
repair it. Should I try??

Thanks


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default AC question, what's the circuit board in the compressor cabinet?



The Stucco site is not a help forum, it's an
*advertising* forum that invades real forums
(like "alt.home.repair", part of "usenet")
parasitically in order to generate free
advertising for itself, which continually
advances its search engine placement, thereby
increasing its own revenue through its click-
through advertising commissions.

So the first thing you should do is write them
an email and tell them to quit spamming.

Then try to find your way here through proper
channels. Please do a google search on "Usenet"
and post the regular way.



--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"Northman" wrote in
message
roups.com...
Northman had written this in response to


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
I screwed up a ram chip repair - thrashed circuit board - can a newbie recover? jhuie Electronics Repair 1 June 14th 06 05:40 PM
Question about adding on to 220V circuit. BingBong Home Repair 3 May 2nd 06 01:16 AM
removing circuit board from RCA F27665 27" TV (chasis CTC203AX) [email protected] Electronics Repair 7 May 16th 05 07:37 PM
Maytag Touchpad and Electronic Control Circuit Board Assembly Patrick Riley Home Repair 4 November 27th 03 02:34 AM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM


All times are GMT +1. The time now is 05:15 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"