DIYbanter

DIYbanter (https://www.diybanter.com/)
-   Home Repair (https://www.diybanter.com/home-repair/)
-   -   Double Pole Circuit Breakers (https://www.diybanter.com/home-repair/165394-double-pole-circuit-breakers.html)

[email protected] June 12th 06 12:05 PM

Double Pole Circuit Breakers
 
I understand that double pole circuit breakers feed 240v (two120's) to
water heaters, stoves, ect...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?
I never worked with 240V circuits before, obviosly. I just need to
install a small baseboard heater in my shop for the upcoming winters;
it calls for a 20A 240v breaker.

Another quick question, but off topic:
Why don't wire manufactures insulate the bare ground wire inside romex
cables?


RBM June 12th 06 12:09 PM

Double Pole Circuit Breakers
 
Each pole of a breaker, single, double or triple, provides the amperage
marked on the breaker. Double pole 20 amp gives you 20 amps on each legs or
20 amps @240 volts
I too, would like the ground wires to be insulated for my own safety



wrote in message
ups.com...
I understand that double pole circuit breakers feed 240v (two120's) to
water heaters, stoves, ect...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?
I never worked with 240V circuits before, obviosly. I just need to
install a small baseboard heater in my shop for the upcoming winters;
it calls for a 20A 240v breaker.

Another quick question, but off topic:
Why don't wire manufactures insulate the bare ground wire inside romex
cables?




Calvin Henry-Cotnam June 12th 06 12:37 PM

Double Pole Circuit Breakers
 
) said...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?


Overcurrent protection is placed on the hot side of a circuit, so with
120V circuits, there is only a single pole breaker for the single hot.

On a 240V circuit, you get 120 volts (relative to the neutral) per
hot (from separate legs). The current that goes through one returns
through the other. Overcurrent protection is needed on BOTH hots and
must be rated the same because it is the SAME current that passes through
both.

Since the voltage is doubled, even though the current is the same, the
POWER that can be provided by the circuit is doubled.

A neutral conductor is only needed on a 240V circuit if there are loads
that require only 120V on the circuit. In those cases, the neutral will
carry the DIFFERENCE between the current in each hot. (e.g.: if one hot
had a current of 10A and the other had 9A, the neutral would be carrying
the 1A difference).

Why don't wire manufactures insulate the bare ground wire inside romex
cables?


Why bother? There is really no safety issue as it only serves to bond
metal chassis and boxes to ground. It will carry a current in fault
situations, but no greater than the overcurrent protection on the circuit.

However, in the case of those ORANGE outlets, the ground pin on the
receptacle is ISOLATED from the bare ground that the box is bonded by.
A separate INSULATED ground conductor is needed to bond the ground pin
to the grounding bus in the panel. Often the red conductor of a 3-wire
cable is used for this purpose.

--
Calvin Henry-Cotnam
"I really think Canada should get over to Iraq as quickly as possible"
- Paul Martin - April 30, 2003
-------------------------------------------------------------------------
NOTE: if replying by email, remove "remove." and ".invalid"


--
Posted via a free Usenet account from
http://www.teranews.com


Doug Miller June 12th 06 12:46 PM

Double Pole Circuit Breakers
 
In article . com, wrote:
I understand that double pole circuit breakers feed 240v (two120's) to
water heaters, stoves, ect...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?


Depends on how it's wired, actually. A double-pole breaker can provide one
240V circuit, or two 120V circuits. In your example, a 30A double-pole breaker
will provide one 30A circuit at 240V, or two 30A circuits at 120V.

Another quick question, but off topic:
Why don't wire manufactures insulate the bare ground wire inside romex
cables?


Because it would be pointless to do so. The grounding wire is intended to
insure that the metal frames of equipment (e.g. a washing machine) and exposed
metal components of the premises wiring (e.g. conduits or receptacle boxes)
are grounded and cannot become live. In other words -- it's connected to
things that are not insulated anyway, and thus no purpose would be served by
insulating it.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

Doug Miller June 12th 06 12:47 PM

Double Pole Circuit Breakers
 
In article , "RBM" rbm2(remove wrote:
Each pole of a breaker, single, double or triple, provides the amperage
marked on the breaker. Double pole 20 amp gives you 20 amps on each legs or
20 amps @240 volts
I too, would like the ground wires to be insulated for my own safety


How would insulating the ground wire improve safety?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

Joseph Meehan June 12th 06 01:11 PM

Double Pole Circuit Breakers
 
wrote:
I understand that double pole circuit breakers feed 240v (two120's) to
water heaters, stoves, ect...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?
I never worked with 240V circuits before, obviosly. I just need to
install a small baseboard heater in my shop for the upcoming winters;
it calls for a 20A 240v breaker.


In short you don't add the amps together you add the voltages together.
So
30A @ 120V
+ 30A @ 120V
______________
30A @ 240V


Another quick question, but off topic:
Why don't wire manufactures insulate the bare ground wire inside romex
cables?


--
Joseph Meehan

Dia duit



Tom The Great June 12th 06 02:16 PM

Double Pole Circuit Breakers
 
On Mon, 12 Jun 2006 07:09:40 -0400, "RBM" rbm2(remove
wrote:

Each pole of a breaker, single, double or triple, provides the amperage
marked on the breaker. Double pole 20 amp gives you 20 amps on each legs or
20 amps @240 volts
I too, would like the ground wires to be insulated for my own safety


imho:

Ground Wires 'do not' carry current except under ground fault
conditions. In that case, the breaker/fuse will break the circuit
asap(by design).

So it normally carries 0 voltage, 0 current.

hth,

tom



wrote in message
oups.com...
I understand that double pole circuit breakers feed 240v (two120's) to
water heaters, stoves, ect...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?
I never worked with 240V circuits before, obviosly. I just need to
install a small baseboard heater in my shop for the upcoming winters;
it calls for a 20A 240v breaker.

Another quick question, but off topic:
Why don't wire manufactures insulate the bare ground wire inside romex
cables?



Toller June 12th 06 02:34 PM

Double Pole Circuit Breakers
 

"Tom The Great" wrote in message
...
On Mon, 12 Jun 2006 07:09:40 -0400, "RBM" rbm2(remove
wrote:

Each pole of a breaker, single, double or triple, provides the amperage
marked on the breaker. Double pole 20 amp gives you 20 amps on each legs
or
20 amps @240 volts
I too, would like the ground wires to be insulated for my own safety


imho:

Ground Wires 'do not' carry current except under ground fault
conditions. In that case, the breaker/fuse will break the circuit
asap(by design).

So it normally carries 0 voltage, 0 current.

You are correct that it normally carries nothing, but why would a breaker
open on a ground fault? (unless it is a gfci...)



[email protected] June 12th 06 02:34 PM

Double Pole Circuit Breakers
 
On Mon, 12 Jun 2006 11:46:52 GMT, (Doug Miller)
wrote:

In article . com,
wrote:
I understand that double pole circuit breakers feed 240v (two120's) to
water heaters, stoves, ect...

But, Im confused about the amperage marking on the middle tab; I see
that most say 30A. Does that mean the each pole from that circuit
breaker can handle up to 30A each pole? 30 + 30 = 60A total? or is the
amps on each hot leg split into two; 15 amps each pole; 15 + 15 = 30A?


Depends on how it's wired, actually. A double-pole breaker can provide one
240V circuit, or two 120V circuits. In your example, a 30A double-pole breaker
will provide one 30A circuit at 240V, or two 30A circuits at 120V.

Another quick question, but off topic:
Why don't wire manufactures insulate the bare ground wire inside romex
cables?


Because it would be pointless to do so. The grounding wire is intended to
insure that the metal frames of equipment (e.g. a washing machine) and exposed
metal components of the premises wiring (e.g. conduits or receptacle boxes)
are grounded and cannot become live. In other words -- it's connected to
things that are not insulated anyway, and thus no purpose would be served by
insulating it.


That's one thing people often do not understand. If you have a 100A
service and only use 120V items in the house, you can actually draw
200A. But if you have all 240V appliances, you can only use 100A. Of
course most homes have both, so that's where the mathematics comes
into play.

Mark

Chris Lewis June 12th 06 02:47 PM

Double Pole Circuit Breakers
 
According to Toller :

You are correct that it normally carries nothing, but why would a breaker
open on a ground fault? (unless it is a gfci...)


A ground fault is simply a leak to the grounding conductor - it could
be a few milliamps, or many amps.

Breakers trip on big ones. GFCIs trip on small ones.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.

J. Clarke June 12th 06 04:52 PM

Double Pole Circuit Breakers
 
Chris Lewis wrote:

According to Toller :

You are correct that it normally carries nothing, but why would a breaker
open on a ground fault? (unless it is a gfci...)


A ground fault is simply a leak to the grounding conductor - it could
be a few milliamps, or many amps.


A ground fault is a leak to ground. It may or may not pass through the
grounding conductor.

Breakers trip on big ones. GFCIs trip on small ones.


Breakers trip on excessive current regardless of the path that it takes.
GFCIs trip on an unbalance between the two wires that compose the active
circuit.

--
--John
to email, dial "usenet" and validate
(was jclarke at eye bee em dot net)

Toller June 12th 06 08:31 PM

Double Pole Circuit Breakers
 

"Pete C." wrote in message
...
wrote:

That's one thing people often do not understand. If you have a 100A
service and only use 120V items in the house, you can actually draw
200A. But if you have all 240V appliances, you can only use 100A. Of
course most homes have both, so that's where the mathematics comes
into play.

Mark


The total power is the same either way or in combination.

100A x 240V = 24,000W
or
200A x 120V = 24,000W
or
50A x 240V = 12,000W
+
100A x 120V = 12,000W
=
24,000W total
etc...

If you happen to have a perfectly balanced system, which is most unlikely...



Pete C. June 12th 06 09:56 PM

Double Pole Circuit Breakers
 
Toller wrote:

"Pete C." wrote in message
...
wrote:

That's one thing people often do not understand. If you have a 100A
service and only use 120V items in the house, you can actually draw
200A. But if you have all 240V appliances, you can only use 100A. Of
course most homes have both, so that's where the mathematics comes
into play.

Mark


The total power is the same either way or in combination.

100A x 240V = 24,000W
or
200A x 120V = 24,000W
or
50A x 240V = 12,000W
+
100A x 120V = 12,000W
=
24,000W total
etc...

If you happen to have a perfectly balanced system, which is most unlikely...


It makes no difference how balanced or unbalanced you have the system,
you will not be pulling more than 24,000W at least not for more than a
few min before the main breaker trips.

It could well be less than that number if you max out one leg first. You
need to have the system balanced to reach the 24,000W load, but the
total amount of power available from the service is 24,000W no matter
what.

Pete C.

RBM June 13th 06 01:46 AM

Double Pole Circuit Breakers
 
If they were insulated, I wouldn't have to be so careful while flailing them
around inside panel boxes
"Doug Miller" wrote in message
y.net...
In article , "RBM" rbm2(remove
wrote:
Each pole of a breaker, single, double or triple, provides the amperage
marked on the breaker. Double pole 20 amp gives you 20 amps on each legs
or
20 amps @240 volts
I too, would like the ground wires to be insulated for my own safety


How would insulating the ground wire improve safety?

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.




unknown June 13th 06 04:19 AM

Double Pole Circuit Breakers
 
On Mon, 12 Jun 2006 20:56:43 GMT, "Pete C."
wrote:

Toller wrote:

"Pete C." wrote in message
...
wrote:

That's one thing people often do not understand. If you have a 100A
service and only use 120V items in the house, you can actually draw
200A. But if you have all 240V appliances, you can only use 100A. Of
course most homes have both, so that's where the mathematics comes
into play.

Mark

The total power is the same either way or in combination.

100A x 240V = 24,000W
or
200A x 120V = 24,000W
or
50A x 240V = 12,000W
+
100A x 120V = 12,000W
=
24,000W total
etc...

If you happen to have a perfectly balanced system, which is most unlikely...


It makes no difference how balanced or unbalanced you have the system,
you will not be pulling more than 24,000W at least not for more than a
few min before the main breaker trips.

It could well be less than that number if you max out one leg first. You
need to have the system balanced to reach the 24,000W load, but the
total amount of power available from the service is 24,000W no matter
what.


Limited to 12,000W per side.

Pete C.


Tom The Great June 13th 06 11:09 PM

Double Pole Circuit Breakers
 
On Mon, 12 Jun 2006 13:34:31 GMT, "Toller" wrote:


"Tom The Great" wrote in message
.. .
On Mon, 12 Jun 2006 07:09:40 -0400, "RBM" rbm2(remove
wrote:

Each pole of a breaker, single, double or triple, provides the amperage
marked on the breaker. Double pole 20 amp gives you 20 amps on each legs
or
20 amps @240 volts
I too, would like the ground wires to be insulated for my own safety


imho:

Ground Wires 'do not' carry current except under ground fault
conditions. In that case, the breaker/fuse will break the circuit
asap(by design).

So it normally carries 0 voltage, 0 current.

You are correct that it normally carries nothing, but why would a breaker
open on a ground fault? (unless it is a gfci...)



If a hot comes in contact with a metal casing, that is grounded, it is
called a ground fault. Following the NEC all grounded equipment
conductors (the ground wire) have to have as lose impedance to
electricy back to the source.

So using ohms law E=IR

E is electrical potencial, or Voltage
I is current
R is resistance.

Solve for I (current) results in I = E/R

substitute numbers for lowest norm voltage. I = 120 / ~0

*Note: Used 0 since a small house has almost 0 ohms back to the panel
on the ground wires.

So calc Current, and you have an almost infinite amount of current, a
short, and the breaker will open on this ground.

A normal breaker should open on any ground fault over thier set
points. Meaning a 15 amp breaker should open on any ground faults
over 15 amps, on over current protection. Ofcourse an almost infinite
current, should trip the breaker on short circuit protection.

hth, (please ignore spelling errors)

tom

~^Johnny^~ June 23rd 06 07:37 AM

Double Pole Circuit Breakers
 
On Mon, 12 Jun 2006 08:34:35 -0500, wrote:

That's one thing people often do not understand. If you have a 100A
service and only use 120V items in the house, you can actually draw
200A.



No way.

Your total load calc may be 200 A at 120 V, but you are still
pulling 100 amps. You've got two 120 volt loads in series, that's
all. You are STILl pulling 100 amps at 240 volts.
Since the individual loads are in series/parallel, they share half teh
voltage, so the total load calc comes out to 200 amps, but only 100
amps are flowing through the service. Really.


--
-john
wide-open at throttle dot info

Doug Miller June 23rd 06 02:22 PM

Double Pole Circuit Breakers
 
In article , ~^Johnny^~ wrote:
On Mon, 12 Jun 2006 08:34:35 -0500, wrote:

That's one thing people often do not understand. If you have a 100A
service and only use 120V items in the house, you can actually draw
200A.



No way.

Your total load calc may be 200 A at 120 V, but you are still
pulling 100 amps. You've got two 120 volt loads in series, that's
all. You are STILl pulling 100 amps at 240 volts.


Which is exactly the same electrical power as 200A at 120V.

Since the individual loads are in series/parallel, they share half teh
voltage, so the total load calc comes out to 200 amps, but only 100
amps are flowing through the service. Really.


100A at 240V -- and, as noted above, if only 120V loads are in use, the total
current draw is (up to) 200A at 120V.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

~^Johnny^~ June 23rd 06 04:11 PM

Double Pole Circuit Breakers
 
On Fri, 23 Jun 2006 13:22:41 GMT, (Doug Miller)
wrote:

100A at 240V -- and, as noted above, if only 120V loads are in use, the total
current draw is (up to) 200A at 120V.


The power consumption is equivalent to 200A at 120V,
but only 100A are flowing. Kirchoff's Law will not
be violated!

Currents in series do not add; =voltages= add.
It's still 100A at 240V.


--
-john
wide-open at throttle dot info

~^Johnny^~ June 23rd 06 04:49 PM

Double Pole Circuit Breakers
 
On Fri, 23 Jun 2006 08:11:40 -0700, ~^Johnny^~
wrote:

On Fri, 23 Jun 2006 13:22:41 GMT, (Doug Miller)
wrote:

100A at 240V -- and, as noted above, if only 120V loads are in use, the total
current draw is (up to) 200A at 120V.



The power consumption is equivalent to 200A at 120V,
but only 100A are flowing. Kirchoff's Law will not
be violated!

Currents in series do not add; =voltages= add.
It's still 100A at 240V.


Better yet,
Look at it this way: If I hang ten 12V lamps in series across a 120V
line, and each lamp is 120 watts, am I pulling a total of 100 amps?
I am not! I am drawing ten amps! Each lamp gets 12V at 10A. 100A
doesn't ever flow, anywhere in the circuit. But I'm still consuming
1200W: 120V at 10A, _NOT_ 12V at 100A. If the lamps were in
parallel, they would require 100A at 12V. But they're not. That's a
load calculation only.

An Edison circuit is just a 240 volt circuit with a grounded
center-tap. In theory, if loads are balanced, the neutral drops out
of the circuit, as the individial loads become a series-parallel
voltage divider network. Each load receives 120V at its rated =power=.



--
-john
wide-open at throttle dot info

Jimmie D June 24th 06 03:30 PM

Double Pole Circuit Breakers
 

"~^Johnny^~" wrote in message
...
On Fri, 23 Jun 2006 08:11:40 -0700, ~^Johnny^~
wrote:

On Fri, 23 Jun 2006 13:22:41 GMT, (Doug Miller)
wrote:

100A at 240V -- and, as noted above, if only 120V loads are in use, the
total
current draw is (up to) 200A at 120V.



The power consumption is equivalent to 200A at 120V,
but only 100A are flowing. Kirchoff's Law will not
be violated!

Currents in series do not add; =voltages= add.
It's still 100A at 240V.


Better yet,
Look at it this way: If I hang ten 12V lamps in series across a 120V
line, and each lamp is 120 watts, am I pulling a total of 100 amps?
I am not! I am drawing ten amps! Each lamp gets 12V at 10A. 100A
doesn't ever flow, anywhere in the circuit. But I'm still consuming
1200W: 120V at 10A, _NOT_ 12V at 100A. If the lamps were in
parallel, they would require 100A at 12V. But they're not. That's a
load calculation only.

An Edison circuit is just a 240 volt circuit with a grounded
center-tap. In theory, if loads are balanced, the neutral drops out
of the circuit, as the individial loads become a series-parallel
voltage divider network. Each load receives 120V at its rated =power=.



--
-john
wide-open at throttle dot info


Assume you have a 200 amp 240 vac breaker with max load, you measure the
current on each leg and it is 200amps.This DOES NOT add up to 400 amps. The
current you measure on one leg is the SAME current you are measuring on the
other leg. Dont confuse same as meaning equal. Same means same as in you
read the curent on a conductor and slide the clamp on amp meter down the
wire a couple of inches and read the SAME current again.

If the currents in each side are not equal then the current in the low side
combined with the current in the neutral will be the SAME as the current in
the high side.. Kirchoff's law explains this a lot more easily using math
than English.




All times are GMT +1. The time now is 08:20 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter