I have to locate a breaker for an outlet, maybe two if they are are
separate breakers. I know where the panel(s) are, but not which breaker controls the outlet. I can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? If the risk is low, what's the best way to short it out? I was thining of a plug where I stripped the two wires, tied them together and taped the end. Anything better? -- cahrles |
#2
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Charles Bishop wrote:
I have to locate a breaker for an outlet, maybe two if they are are separate breakers. I know where the panel(s) are, but not which breaker controls the outlet. I can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? If the risk is low, what's the best way to short it out? I was thining of a plug where I stripped the two wires, tied them together and taped the end. Anything better? -- cahrles The best way to find this is with one of the electronic tracker setups, or a pulsating load (light with a flasher) and a clamp on amp probe. The shorting method will work (I've done it in a pinch) but it's not pretty. The safest way would be to wire a switch in a proper electrical box to a short cord with a plug. This protects you and the outlet from the arc and lets you use an old junk switch if you have one to take the abuse. Circuit breakers can have their trip points drift (generally lower) with repeated trips so you don't want to do it more than once if you can help it. Pete C. |
#3
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Charles Bishop wrote:
I have to locate a breaker for an outlet, maybe two if they are are separate breakers. I know where the panel(s) are, but not which breaker controls the outlet. I can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? If the risk is low, what's the best way to short it out? I was thining of a plug where I stripped the two wires, tied them together and taped the end. Anything better? I would avoid shorting it out. If everything is working right, it will be OK, it is also possible that you may find a weak link in the system. Stop by the the tool store and get a tool to hunt it down. Note: even after you have identified it, double check that after turning off that circuit that both outlets are now dead, as you wisely indicated, they may not be on the same circuit. -- Joseph Meehan Dia duit |
#4
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "Charles Bishop" wrote in message ... I have to locate a breaker for an outlet, maybe two if they are are separate breakers. I know where the panel(s) are, but not which breaker controls the outlet. I can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. Have you checked to see if the panel(s) are labeled? How do you know that the circuit that you want to trip is not also powering the other equipment that you want to keep on? What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? Maybe damaging a breaker? Doesn't happen real often but is a possibility. I have had to replace breakers for people after a short or miswire. After finding and correcting the fault, the breaker would not reset and had to be replaced. Sometimes the main will also trip on a dead short. Kevin If the risk is low, what's the best way to short it out? I was thining of a plug where I stripped the two wires, tied them together and taped the end. Anything better? -- cahrles |
#5
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
CB asked:
What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? Ray replied: Burned fingers Electrocution Fire Melted insulation that will short later Damage to other appliances on that circuit Damaged breaker Probably none of these things will happen but if you really insist on doing this it would probably be *slightly* safer to strip the ends of an old plug and touch them together briefly while holding the ends with rubber handled pliers. If you plug in something hard-wired to short and the breaker doesn't trip, now you have to pull it out before the fire starts. CB also said: ....can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. Ray asked: What happens when the power goes out? You have about a 50/50 chance of shutting off the outlet before the 'other equipment'. I'd take those odds over intentionaly shorting an outlet... |
#6
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() Probably none of these things will happen but if you really insist on doing this it would probably be *slightly* safer to strip the ends of an old plug and touch them together briefly while holding the ends with rubber handled pliers. He says as molten metal sprays his face and hands I find a toaster oven and microwave oven running at the same time is a relaible and safe way to trip a breaker (typical 20A) |
#7
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
In article .com,
RayV wrote: CB asked: What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? Ray replied: Burned fingers Electrocution Fire Melted insulation that will short later Damage to other appliances on that circuit Damaged breaker Probably none of these things will happen but if you really insist on doing this it would probably be *slightly* safer to strip the ends of an old plug and touch them together briefly while holding the ends with rubber handled pliers. If you plug in something hard-wired to short and the breaker doesn't trip, now you have to pull it out before the fire starts. Depending on the quality of the short, and the trip rating of all the breakers in the path, it is possible for a bolted fault on a branch circuit to trip the main breaker. I have seen it happen, with a 20a 240v circuit (wired as a dead short between two phases*), that tripped a 400a main breaker with no hesitation. In this case, the 20a breaker was closed into the short, and the main tripped in the blink of an eye. (* when wiring a 240 volt outlet, you DO NOT attach both phases to one terminal, and the neutral to another. The stage carpenter didn't know this.. needless to say, he does now..) -- -- Welcome My Son, Welcome To The Machine -- Bob Vaughan | techie @ tantivy.net | | P.O. Box 19792, Stanford, Ca 94309 | -- I am Me, I am only Me, And no one else is Me, What could be simpler? -- |
#8
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() |
#9
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 9 May 2006 05:38:43 -0700, "RayV" wrote:
CB asked: What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? Ray replied: Burned fingers Electrocution Fire Melted insulation that will short later Damage to other appliances on that circuit Damaged breaker Probably none of these things will happen but if you really insist on doing this it would probably be *slightly* safer to strip the ends of an old plug and touch them together briefly while holding the ends with rubber handled pliers. If you plug in something hard-wired to short and the breaker doesn't trip, now you have to pull it out before the fire starts. How about using a momentary contact pushbutton switch? CB also said: ...can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. Ray asked: What happens when the power goes out? You have about a 50/50 chance of shutting off the outlet before the 'other equipment'. I'd take those odds over intentionaly shorting an outlet... -- Mark Lloyd http://notstupid.laughingsquid.com "Democracy is two wolves and a lamb voting on what to have for lunch. Liberty is a well armed lamb contesting the vote." - Benjamin Franklin |
#10
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
You could plug in two heat devices (hair dryer plus space heater) and
trip the breaker that way. -- Christopher A. Young You can't shout down a troll. You have to starve them. .. "RayV" wrote in message oups.com... CB asked: What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? |
#11
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it?
Depending on "how", not much. In fact you could earn a Darwin Award in the process if done correctly. Written with tongue planted firmly into cheek ;-) DAC |
#12
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
I have used the short outlet to find breaker method. POnce I found a
bad breaker that never tripped, and melted the wiring. no biggie for me but perhapos a deal breaker for you. If your main panel has FPE stab lock breakers DONT USE THE SHORT METHOD. Once a FPE breaker has tripped on a short it may never trip again. REPL:ACE THE PANEL ASAP! Just whats so important you cant shut off breakers? the power company has popwer failures, so everything is designed to tolerate power offs. plug a radio in the outlets with volume up high then trip breakers one at a time till the radio quits. safest best method...... do when no one else is home, most that can happen is some flashing 12;00 CLOCKS dont tell anyone they will nver know.... thinking house just had power failure ![]() Its best to check every device in home and make a breaker chart so you know in the future |
#13
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() wrote in message oups.com... I have used the short outlet to find breaker method. POnce I found a bad breaker that never tripped, and melted the wiring. no biggie for me but perhapos a deal breaker for you. If your main panel has FPE stab lock breakers DONT USE THE SHORT METHOD. Once a FPE breaker has tripped on a short it may never trip again. REPL:ACE THE PANEL ASAP! Just whats so important you cant shut off breakers? the power company has popwer failures, so everything is designed to tolerate power offs. plug a radio in the outlets with volume up high then trip breakers one at a time till the radio quits. safest best method...... do when no one else is home, most that can happen is some flashing 12;00 CLOCKS dont tell anyone they will nver know.... thinking house just had power failure ![]() Its best to check every device in home and make a breaker chart so you know in the future Fair enough, if he had life critical equipment like a medical ventilator or monitor, those things should be on a UPS. Same for a website server etc. |
#14
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Likely a toaster and a hair dryer on full power will draw enough current to
trip the breaker. "Charles Bishop" wrote in message ... I have to locate a breaker for an outlet, maybe two if they are are separate breakers. I know where the panel(s) are, but not which breaker controls the outlet. I can't shut off the breakers until I find it since there is other equipment that I don't want to shut down. What am I risking by "shorting" out the outlet and having it trip the breaker so I can find it? If the risk is low, what's the best way to short it out? I was thining of a plug where I stripped the two wires, tied them together and taped the end. Anything better? -- cahrles |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Can a breaker open without showing the orange tab? | Home Repair | |||
Elec info needed 20A circuits | Home Repair | |||
Dryer flips main circuit breaker occasionally | Home Repair | |||
can a circuit re-enter the breaker box? | Home Repair | |||
breaker tripping | Home Repair |