Hello,

I'm planning to run an electrical circuit outdoors for the first time
(with permit and inspections), and I was hoping someone with more
experience could tell me if my plans sound OK. For simplicity I'm
going to run NM cable and sheath it in appropriately sized conduit.

Run 6" RMC nipple through sidewall of crawl space into the back of a
wet locations outlet box. Cap ends with insulating bushings. Makeup
connections, ground the box, and install switch plus wet locations
switch cover with gasket. Run about 2' of NM liquid tight conduit
from the outlet box to the device (exterior tankless water heater),
using liquid tight connectors to make the connections. Makeup the
connections and ground the device. Seal house penetrations and the
outlet plugs for unused ports with 100% silicone.

Sounds OK? Also, a few more assumptions: no locknut is required when
attaching a threaded connector to the threaded ports on the outlet
box. The RMC nipple to outlet box connection should get silicone, as
there is no gasket, and the silicone will not interfere with the
ground bond. Are these assumptions correct?

Thanks, Wayne

P.S. Is RMC identical to iron pipe for water?
  #2   Report Post  
Posted to alt.home.repair
SQLit
 
Posts: n/a
Default Outdoor electrical circuit install check


"Wayne Whitney" wrote in message
...
Hello,

I'm planning to run an electrical circuit outdoors for the first time
(with permit and inspections), and I was hoping someone with more
experience could tell me if my plans sound OK. For simplicity I'm
going to run NM cable and sheath it in appropriately sized conduit.

Run 6" RMC nipple through sidewall of crawl space into the back of a
wet locations outlet box. Cap ends with insulating bushings. Makeup
connections, ground the box, and install switch plus wet locations
switch cover with gasket. Run about 2' of NM liquid tight conduit
from the outlet box to the device (exterior tankless water heater),
using liquid tight connectors to make the connections. Makeup the
connections and ground the device. Seal house penetrations and the
outlet plugs for unused ports with 100% silicone.

Sounds OK? Also, a few more assumptions: no locknut is required when
attaching a threaded connector to the threaded ports on the outlet
box. The RMC nipple to outlet box connection should get silicone, as
there is no gasket, and the silicone will not interfere with the
ground bond. Are these assumptions correct?

Thanks, Wayne

P.S. Is RMC identical to iron pipe for water?



NM Flex does not last but a few years in the sun, where I live. (Phoenix)

Check to see if the switch has an interrupting capacity of at least the load
in the heater. (20 amp)

Electrical conduit has a tapered thread GRC for plumbing has a straight
thread. Other than that the two are interchanged frequently where I live
especially for nipples.

I do not under stand your grounding assumptions cause you do not state from
where the grc nipple starts.


  #3   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default Outdoor electrical circuit install check

Pipe threads are tapered also.

"SQLit" wrote in message
news

"Wayne Whitney" wrote in message
...
Hello,

I'm planning to run an electrical circuit outdoors for the first time
(with permit and inspections), and I was hoping someone with more
experience could tell me if my plans sound OK. For simplicity I'm
going to run NM cable and sheath it in appropriately sized conduit.

Run 6" RMC nipple through sidewall of crawl space into the back of a
wet locations outlet box. Cap ends with insulating bushings. Makeup
connections, ground the box, and install switch plus wet locations
switch cover with gasket. Run about 2' of NM liquid tight conduit
from the outlet box to the device (exterior tankless water heater),
using liquid tight connectors to make the connections. Makeup the
connections and ground the device. Seal house penetrations and the
outlet plugs for unused ports with 100% silicone.

Sounds OK? Also, a few more assumptions: no locknut is required when
attaching a threaded connector to the threaded ports on the outlet
box. The RMC nipple to outlet box connection should get silicone, as
there is no gasket, and the silicone will not interfere with the
ground bond. Are these assumptions correct?

Thanks, Wayne

P.S. Is RMC identical to iron pipe for water?



NM Flex does not last but a few years in the sun, where I live. (Phoenix)

Check to see if the switch has an interrupting capacity of at least the
load
in the heater. (20 amp)

Electrical conduit has a tapered thread GRC for plumbing has a straight
thread. Other than that the two are interchanged frequently where I live
especially for nipples.

I do not under stand your grounding assumptions cause you do not state

from
where the grc nipple starts.




  #4   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Outdoor electrical circuit install check

Sounds fine, the only possible issue might be: NM cable and the wire inside
it, is not for use in wet locations. The whip from your switch to the heater
may be considered a wet location. You can use TW or THWN in wet locations



"Wayne Whitney" wrote in message
...
Hello,

I'm planning to run an electrical circuit outdoors for the first time
(with permit and inspections), and I was hoping someone with more
experience could tell me if my plans sound OK. For simplicity I'm
going to run NM cable and sheath it in appropriately sized conduit.

Run 6" RMC nipple through sidewall of crawl space into the back of a
wet locations outlet box. Cap ends with insulating bushings. Makeup
connections, ground the box, and install switch plus wet locations
switch cover with gasket. Run about 2' of NM liquid tight conduit
from the outlet box to the device (exterior tankless water heater),
using liquid tight connectors to make the connections. Makeup the
connections and ground the device. Seal house penetrations and the
outlet plugs for unused ports with 100% silicone.

Sounds OK? Also, a few more assumptions: no locknut is required when
attaching a threaded connector to the threaded ports on the outlet
box. The RMC nipple to outlet box connection should get silicone, as
there is no gasket, and the silicone will not interfere with the
ground bond. Are these assumptions correct?

Thanks, Wayne

P.S. Is RMC identical to iron pipe for water?



  #5   Report Post  
Posted to alt.home.repair
Wayne Whitney
 
Posts: n/a
Default Outdoor electrical circuit install check

On 2006-01-28, SQLit wrote:

NM Flex does not last but a few years in the sun, where I
live. (Phoenix)


Thanks for your comments. What do you suggest as an alternative?

Check to see if the switch has an interrupting capacity of at least
the load in the heater. (20 amp)


The gas tankless unit is a Noritz N-063S-OD, and its manual says the
maximum power draw is 125W (when freeze protection kicks in, otherwise
it is 65W). So any switch should be rated for 1 amp. And as I
understand, there is no need for a switch to be rated at the circuit
amperage, just the load amperage?

I do not under stand your grounding assumptions cause you do not
state from where the grc nipple starts.


I mentioned I'm running NM cable and the conduit is just to protect it
from the elements. So I'm going to depend on grounding the box to
ground the nipple, the other end of the nipple in the crawl space
isn't attached to anything. My question was whether using silicone to
seal the connection between the nipple and the box will keep the
nipple from being grounded. I can always test the resistance
afterwards with a multimeter, is that sufficient?

Cheers, Wayne



  #6   Report Post  
Posted to alt.home.repair
Wayne Whitney
 
Posts: n/a
Default Outdoor electrical circuit install check

On 2006-01-28, RBM wrote:

Sounds fine, the only possible issue might be: NM cable and the wire
inside it, is not for use in wet locations. The whip from your
switch to the heater may be considered a wet location. You can use
TW or THWN in wet locations


Interesting question, I assumed that the inside of a liquidtight
conduit would be considered a dry location. I see that I do have
enough spare THWN lying around, so I'll use it. Thanks.

Is it OK to run the NM cable into the exterior box, or should I switch
to THWN before leaving the house? I'd prefer to avoid another
junction box.

Cheers, Wayne

  #7   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Outdoor electrical circuit install check

The box on the house is fine. In my opinion, the whip is fine too. I've just
had some real particular inspectors give me grief about conductor types in
outdoor conduits


"Wayne Whitney" wrote in message
...
On 2006-01-28, RBM wrote:

Sounds fine, the only possible issue might be: NM cable and the wire
inside it, is not for use in wet locations. The whip from your
switch to the heater may be considered a wet location. You can use
TW or THWN in wet locations


Interesting question, I assumed that the inside of a liquidtight
conduit would be considered a dry location. I see that I do have
enough spare THWN lying around, so I'll use it. Thanks.

Is it OK to run the NM cable into the exterior box, or should I switch
to THWN before leaving the house? I'd prefer to avoid another
junction box.

Cheers, Wayne



  #8   Report Post  
Posted to alt.home.repair
Wayne Whitney
 
Posts: n/a
Default Outdoor electrical circuit install check

On 2006-01-28, RBM wrote:

The box on the house is fine. In my opinion, the whip is fine
too. I've just had some real particular inspectors give me grief
about conductor types in outdoor conduits


Well, I just read a long thread about this topic at mikeholt.com. It
comes down to an interpretation of part of NEC Article 225 "Outside
Branch Circuits and Feeders". The second sentence of 225.4 reads:

Conductors in cables or raceways, except Type MI cable, shall be of
the rubber-covered type or thermoplastic type and, in wet locations,
shall comply with 310.8.

310.8 specifies what wire types can be used in wet locations. The
question is whether this sentence means "conductors . . . in wet
locations shall comply with 310.8" or "conductors in cables or
raceways . . . in wet locations shall comply with 310.8". My money is
on the latter interpretation, since the former interpretation just
seems to be a reiteration of 310.8, so there would be no need for the
second half of the sentence.

Anyway, I'll use THWN.

Thanks, Wayne
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chantecler Windows and Doors Brian White Home Repair 3 June 6th 16 11:22 PM
Electrical question: a gfci AND a lighting circuit Home Repair 4 December 9th 05 08:17 PM
What Type Of Surge Protection House Circuit Breaker ? Robert11 Home Repair 9 August 4th 05 04:37 PM
15A Circuit Breaker on a Power Tap Jajal Electronics 3 April 3rd 04 03:18 PM
Typical domestic electrical circuits John Aston UK diy 21 January 21st 04 03:10 PM


All times are GMT +1. The time now is 05:19 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"