Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80
amp breaker.



Thank you

Bill





TURTLE May 26th 05 11:33 PM


"Bill C" wrote in message
. ..

Hello,



Can someone please tell me what AWG copper line is required to service a 68.5
amp 240vac tankless water heater? The manufacturer recommends an 80 amp
breaker.



Thank you

Bill


there is all kinds of type wire to choose from as distance of run and as in
conduit or not and you can run it in # 6 to a # 2 by just what type wire it is
and the metal the wire is made out of.

So if run in Copper wire run # 2 and you can't go wrong. the wire can be smaller
if you tell the conditions like length of run , type of wire you have to use ,
and in conduit or out.

TURTLE



Doug Miller May 27th 05 12:40 AM

In article , "Bill C" wrote:

Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80
amp breaker.


Anywhere between #6 and #2. Depends on the temperature ratings of the
conductors, and how they're installed (cable, conduit, etc).

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?

RBM May 27th 05 01:22 AM

There are variables but generally for what you're looking to do, number 4
THWN
"Bill C" wrote in message
. ..

Hello,



Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80
amp breaker.



Thank you

Bill







Bill C May 27th 05 02:24 AM

Thanks everyone. I don't like my subpanel setup. It's a big mess to
upgrade and a long run in an old house to try to pull new wire. I'll just
replace this failing tank water heater with another tank water heater.

Regards
Bill


"Bill C" wrote in message
. ..

Hello,



Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80
amp breaker.



Thank you

Bill







Stormin Mormon May 27th 05 01:02 PM

Also, copper versus aluminum makes a difference. I don't have a spec sheet,
but alum takes a lower number. Which is a physically larger wire.

--

Christopher A. Young
Learn more about Jesus
www.lds.org
www.mormons.com


"Doug Miller" wrote in message
. ..
In article , "Bill C"
wrote:

Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80
amp breaker.


Anywhere between #6 and #2. Depends on the temperature ratings of the
conductors, and how they're installed (cable, conduit, etc).

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?



zxcvbob May 27th 05 03:24 PM

Stormin Mormon wrote:
Also, copper versus aluminum makes a difference. I don't have a spec sheet,
but alum takes a lower number. Which is a physically larger wire.



He needs ampacity of 85A rather than 68.5 because it's a continuous
resistive load. #3 Aluminum type SE cable will work if the breaker and
terminals are rated for 90°C. Otherwise, he needs #4 copper rated for
75°C or better.