The unit in question is Goodman GMV9509050XBA gas furnace (95% eff.,
90,000 BTU.)
It says in the Installation Instructions (page 7, Location Requirements
& Considerations) that the following must be observed:

"The temperature of the return air entering the furnace is between 55F
and 100F when the furnace is heating."

I am curious why the 55F requirement. I mean, when I'm not in the
house, I would like to set the temp as low as possible in order to save
on my heating bill. I think I could otherwise set it as low as 45-50F
and still keep the water pipes from freezing. But I wonder why I'm not
supposed to go below 55F. What could happen? Could the unit get damaged
and why?

Thanks

P.S. I'm in the Denver, CO area - 5,300 ft altitude, if that matters.

  #3   Report Post  
Posted to sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 255
Default High Efficiency gas furnace - return air temperature

On Fri, 19 Jan 2007 05:59:45 GMT, Tony Hwang wrote:

wrote:
The unit in question is Goodman GMV9509050XBA gas furnace (95% eff.,
90,000 BTU.)
It says in the Installation Instructions (page 7, Location Requirements
& Considerations) that the following must be observed:

"The temperature of the return air entering the furnace is between 55F
and 100F when the furnace is heating."

I am curious why the 55F requirement. I mean, when I'm not in the
house, I would like to set the temp as low as possible in order to save
on my heating bill. I think I could otherwise set it as low as 45-50F
and still keep the water pipes from freezing. But I wonder why I'm not
supposed to go below 55F. What could happen? Could the unit get damaged
and why?

Thanks

P.S. I'm in the Denver, CO area - 5,300 ft altitude, if that matters.

Hi,
I am just guessing. If return air temp. is to low it may not produce
warm enough air. Air is passing thru the heat exchanger at constant
speed and think law of physics.



Blow me.



--
Click here every day to feed an animal that needs you today !!!
http://www.theanimalrescuesite.com/

Paul ( pjm @ pobox . com ) - remove spaces to email me
'Some days, it's just not worth chewing through the restraints.'
'With sufficient thrust, pigs fly just fine.'
HVAC/R program for Palm PDA's
Free demo now available online http://pmilligan.net/palm/
  #4   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 3,515
Default Tony hunglow guessing - who wudda thunk?

Tony Hwang posted for all of us...

I am just guessing.

That is ALL you are capable of; the subject does not matter. Go guess back in
a.h.r you might find a sucker there.
--
Tekkie Don't bother to thank me, I do this as a public service.
  #6   Report Post  
Posted to sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 6,199
Default High Efficiency gas furnace - return air temperature

well lewts say the home is 40 degrees, and moisture is accumulating.
pretty quick the temp should rise, and the moisture go away

perhaps he should call the manufacturer?

long term would more likely be a problem

  #9   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 2
Default High Efficiency gas furnace - return air temperature

It is my understanding that if the return air temperature is too low
the
heat exchanger can be "shocked"--that is to say it may expand and
contract
beyond design limits and fail.

  #10   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
AKS AKS is offline
external usenet poster
 
Posts: 5
Default High Efficiency gas furnace - return air temperature

Any metal will expand and contract with change of temperature
but I do not believe that this problem occurs in low temp.
residential furnaces however anything is possible
Dido

"Redcrosse" wrote in message
ups.com...
It is my understanding that if the return air temperature is too low
the
heat exchanger can be "shocked"--that is to say it may expand and
contract
beyond design limits and fail.





  #11   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 2
Default High Efficiency gas furnace - return air temperature

I am told by experts in the field that one of several ways that
high-efficiency furnaces squeeze more BTU's from their fuels is by
using thinner and thinner heat exchangers that naturally have tighter
tolerances for expansion and contraction. Old coal fired furnaces had
cast iron heat exchangers that could and did last for a very long time.
Most "cracked heat exchangers" in those appliances seem to have been a
salesman's way of getting a customer to buy . . . not an actual crack.
Modern furnaces with crimped stainless steel heat exchangers are often
projected to have a life of 15 years +/-.




AKS wrote:
Any metal will expand and contract with change of temperature
but I do not believe that this problem occurs in low temp.
residential furnaces however anything is possible
Dido

"Redcrosse" wrote in message
ups.com...
It is my understanding that if the return air temperature is too low
the
heat exchanger can be "shocked"--that is to say it may expand and
contract
beyond design limits and fail.


  #12   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default High Efficiency gas furnace - return air temperature

On 22 Jan 2007 06:23:03 -0800, "Edward R. Voytovich"
wrote:

I am told by experts in the field that one of several ways that
high-efficiency furnaces squeeze more BTU's from their fuels is by
using thinner and thinner heat exchangers


This seems like one of the false efficiencies, for the most part.
Although it would take a few seconds, even a minute maybe longer to
heat a thick heat exchanger wall, once it was heated all the way
through, it would be just as efficient as a thin one.

Then at the end of the cycle, there would be more heat left over,
which would disperse, some warming the circulating air which would
continue to be circulated by the fan (until the low-limit thermostat
switched the fan off) and the rest would eventually heat the basement
a little bit, or wherever the furnace was. In the case of my
basement, I need a bit of heat there in the winter, and there is a
heating duct, and the furnace radiates is a small amount but probably
needed for my comfort.

If the furnace were in the garage, well one normally goes to a garage
even less than a basement, but doesn;t the whole furnace radiate heat,
not just the rather small amount in even a thick heat exchanger wall.

that naturally have tighter
tolerances for expansion and contraction. Old coal fired furnaces had
cast iron heat exchangers that could and did last for a very long time.
Most "cracked heat exchangers" in those appliances seem to have been a
salesman's way of getting a customer to buy . . . not an actual crack.
Modern furnaces with crimped stainless steel heat exchangers are often
projected to have a life of 15 years +/-.


Oy.




AKS wrote:
Any metal will expand and contract with change of temperature
but I do not believe that this problem occurs in low temp.
residential furnaces however anything is possible
Dido

"Redcrosse" wrote in message
ups.com...
It is my understanding that if the return air temperature is too low
the
heat exchanger can be "shocked"--that is to say it may expand and
contract
beyond design limits and fail.


  #13   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 4,500
Default High Efficiency gas furnace - return air temperature


mm wrote:
On 22 Jan 2007 06:23:03 -0800, "Edward R. Voytovich"
wrote:

I am told by experts in the field that one of several ways that
high-efficiency furnaces squeeze more BTU's from their fuels is by
using thinner and thinner heat exchangers


This seems like one of the false efficiencies, for the most part.
Although it would take a few seconds, even a minute maybe longer to
heat a thick heat exchanger wall, once it was heated all the way
through, it would be just as efficient as a thin one.


That simply isn't true. The heat is going to transfer more
effectively across the thinner material. The thickness of the metal
provides a resistance to heat flow, just as thicker insulation, wood,
or anything else would.





Then at the end of the cycle, there would be more heat left over,
which would disperse, some warming the circulating air which would
continue to be circulated by the fan (until the low-limit thermostat
switched the fan off) and the rest would eventually heat the basement
a little bit, or wherever the furnace was. In the case of my
basement, I need a bit of heat there in the winter, and there is a
heating duct, and the furnace radiates is a small amount but probably
needed for my comfort.

If the furnace were in the garage, well one normally goes to a garage
even less than a basement, but doesn;t the whole furnace radiate heat,
not just the rather small amount in even a thick heat exchanger wall.

that naturally have tighter
tolerances for expansion and contraction. Old coal fired furnaces had
cast iron heat exchangers that could and did last for a very long time.
Most "cracked heat exchangers" in those appliances seem to have been a
salesman's way of getting a customer to buy . . . not an actual crack.
Modern furnaces with crimped stainless steel heat exchangers are often
projected to have a life of 15 years +/-.


Oy.




AKS wrote:
Any metal will expand and contract with change of temperature
but I do not believe that this problem occurs in low temp.
residential furnaces however anything is possible
Dido

"Redcrosse" wrote in message
ups.com...
It is my understanding that if the return air temperature is too low
the
heat exchanger can be "shocked"--that is to say it may expand and
contract
beyond design limits and fail.


  #14   Report Post  
Posted to alt.hvac,sci.engr.heat-vent-ac,misc.consumers.house,alt.home.repair
external usenet poster
 
Posts: 59
Default High Efficiency gas furnace - return air temperature

Well, the verdict is in. I called a Goodman authorized HVAC
dealer/contractor (in Denver Metro), and their technician told me that
the reason that return air temp must not be less than 55F is because of
the possibility of excess condensation.

BTW, I first called the Goodman hotline, but they told me that, for
liability reasons, they didn't provide tech support directly to
individuals. However, they told me to call one of their authorized
dealers with any questions. They gave me three names, and I called one
of them.

Cheers.


On Jan 18, 10:12 pm, wrote:
The unit in question is Goodman GMV9509050XBA gas furnace (95% eff.,
90,000 BTU.)
It says in the Installation Instructions (page 7, Location Requirements
& Considerations) that the following must be observed:

"The temperature of the return air entering the furnace is between 55F
and 100F when the furnace is heating."

I am curious why the 55F requirement. I mean, when I'm not in the
house, I would like to set the temp as low as possible in order to save
on my heating bill. I think I could otherwise set it as low as 45-50F
and still keep the water pipes from freezing. But I wonder why I'm not
supposed to go below 55F. What could happen? Could the unit get damaged
and why?

Thanks

P.S. I'm in the Denver, CO area - 5,300 ft altitude, if that matters.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
High Efficiency gas furnace - return air temperature [email protected] Home Repair 39 January 27th 07 10:23 AM
high efficiency gas furnace advice please [email protected] Home Repair 17 October 10th 05 05:12 AM
New high-efficiency gas furnace, old hot water tank - any issues? [email protected] Home Repair 5 August 8th 05 11:04 PM
Venting Of A New "High Efficiency" Forced Hot Air Furnace ? Robert11 Home Repair 7 April 6th 05 04:41 AM


All times are GMT +1. The time now is 01:45 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"