Home |
Search |
Today's Posts |
|
#1
|
|||
|
|||
Info to backup safety of aluminum wiring?
I've moved into a house build in 1971 which is wired mainly with
aluminum wiring. I've read a handful of published information that states that aluminum wiring (or more correctly, the connections made with aluminum wiring) do in fact create a fire hazard greater than copper wire. I also know that a lot of people state that aluminum wiring does not pose any greater risk than copper if done properly. What I'm interested in is what is "done properly" and have there been tests done on such "proper" wiring methods to prove that they do in fact pose no increased fire hazard? So in other words, what I'm looking for is published (on paper, internet, etc.) information from reputable sources that would refute the claims made by the information that I've already read making aluminum out to be a fire hazard. A lot of the information I've read so far can be found at www.inspect-ny.com/aluminum.htm Thanks for the input, Harry |
#2
|
|||
|
|||
Make certain you have lots of working smoke detectors while you check
out it's safety. |
#3
|
|||
|
|||
"Harry Muscle" wrote in message ups.com... I've moved into a house build in 1971 which is wired mainly with aluminum wiring. I've read a handful of published information that states that aluminum wiring (or more correctly, the connections made with aluminum wiring) do in fact create a fire hazard greater than copper wire. I also know that a lot of people state that aluminum wiring does not pose any greater risk than copper if done properly. What I'm interested in is what is "done properly" and have there been tests done on such "proper" wiring methods to prove that they do in fact pose no increased fire hazard? So in other words, what I'm looking for is published (on paper, internet, etc.) information from reputable sources that would refute the claims made by the information that I've already read making aluminum out to be a fire hazard. A lot of the information I've read so far can be found at www.inspect-ny.com/aluminum.htm Thanks for the input, Harry I have been installing AL for more than 30 years. There is nothing wrong with the wire. The problems come from the installers and the terminations. If properly terminated there will be no more problems with AL than copper. I do not know of any utilities that use copper any more. All of the long lines and distribution lines in the West are primarily AL. If they were not some maroon would steal them. Which has happened in the old days, 1960-70's. All of that wire was replaced with AL. Your home and mine (also built in 1971) have lasted this long. Chances are they will last a lot more. This is my 3 home of this vintage. Do you know anyone with a 1000 volt meggar? You will need to unplug EVERYTHING for the test. The meggar can tell you if there is an insulation problem and to a point loose connections. Most of the published articles are done by fire departments and the copper association. Unfortunately the fire department only gets to visit when there is a problem. Ideal makes a wire nut for AL-CU connections. About $2 ea at the box stores. Devices should be listed AL-CU and they are harder and harder to find. |
#4
|
|||
|
|||
I live in the midwest and AL wire is used on most new transmission
lines I see. How about homes - I thought AL wiring in homes no longer was approved? When I lived in the south a bunch of "modular homes" factory built with AL wiring burned - had everybody looking at their wires. Thanks for the info on the meggar. |
#5
|
|||
|
|||
The problem with AL wiring in homes is at the connections ...
transmission lines would obvioulsy have very different connection systems in place compared to your average home. There is for example an approved and tested method of making aluminum wire connections to copper wire using an COPALUM tool. Chances are something similar, but on a bigger scale, is done with transmission lines ... however, comparing transmission lines to home wiring, doesn't really prove much since they are such different systems. Thanks, Harry |
#6
|
|||
|
|||
"butch burton" wrote in message oups.com... I live in the midwest and AL wire is used on most new transmission lines I see. How about homes - I thought AL wiring in homes no longer was approved? When I lived in the south a bunch of "modular homes" factory built with AL wiring burned - had everybody looking at their wires. Thanks for the info on the meggar. What really happened was copper went through the roof in price so people started using AL and AL clad copper wire. Let us not go into the copper clad stuff. During the time that copper was high and the less than craftsmen were using the AL romex there were a lot of problems. One contractor where I lived lost his electrical license because of fires. He even burned his own mothers home down. The problem lies in the craftsman pulling the wire and doing the terminations. Using the proper devices, ( switches and recpts ) is also a biggie. I know of lots of "electrical workers" that stabbed the AL wire into the back of the devices. Even though the device instructions said not to with AL wire. ( use the side screws ). Larger AL wire is connected using hydraulic press tools. There are even AL to copper connectors made. I have never seen a hydraulic pressed termination go bad not in 30 years. Providing it was done correctly in the beginning. Today there is a different alloy used and different insulation. New homes today have circuits above 30 amp AL is still used. ( general guideline ). You can spend the money for copper. I doubt that you will see a penny when selling the home. No one cares what is in the walls. People accept plastic flexible water pipes ( general term ) all of the time now days. Some new home builders do not even offer to put in copper water pipes. |
#7
|
|||
|
|||
According to SQLit :
You can spend the money for copper. I doubt that you will see a penny when selling the home. No one cares what is in the walls. People accept plastic flexible water pipes ( general term ) all of the time now days. Some new home builders do not even offer to put in copper water pipes. Having aluminum in your walls is _still_ a significant house price dampener. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#8
|
|||
|
|||
It all depends on the real estate market in your area. I know in my
area, the wiring won't make much difference with the market we have right now ... even knob and tube wired houses sell. I'm willing to accept the fact that whatever money I spend on the wiring will never be recovered. I want to fix things for safety sake mainly. Thanks, Harry |
#9
|
|||
|
|||
SQLit wrote:
What really happened was copper went through the roof in price so people started using AL and AL clad copper wire. Let us not go into the copper clad stuff. During the time that copper was high and the less than craftsmen were using the AL romex there were a lot of problems. One contractor where I lived lost his electrical license because of fires. He even burned his own mothers home down. The problem lies in the craftsman pulling the wire and doing the terminations. Using the proper devices, ( switches and recpts ) is also a biggie. I know of lots of "electrical workers" that stabbed the AL wire into the back of the devices. Even though the device instructions said not to with AL wire. ( use the side screws ). Larger AL wire is connected using hydraulic press tools. There are even AL to copper connectors made. I have never seen a hydraulic pressed termination go bad not in 30 years. Providing it was done correctly in the beginning. Biggest problem was probably the switches and receptacles (although backstabing them would be a real bad idea). After problems developed, UL removed listing on wire and devices in 7-1971. In 9-1971 they started listing devices which are marked CO/ALR. I havn't heard of problems with these devices. If I was using them, I would probably use some anti-oxide paste on the aluminum wire. Bud-- |
#10
|
|||
|
|||
Thank you for the reply. I like your point about the fact that a lot
of the published articles are probably done by fire departments, etc. But taking the example of the Ideal wire nut ... who do I believe. The information presented he www.inspect-ny.com/aluminum/twistcpsc.htm www.inspect-ny.com/aluminum/ideal65.htm www.inspect-ny.com/aluminum/i65debat.htm Or individuals like yourself and others who've never had issues with these connectors in their own homes? Hence my dilema ... Also, as a side point ... what do you consider "properly terminated"? Using AL approved outlets and switches, pigtailing, etc.? Thanks, Harry |
#11
|
|||
|
|||
"Harry Muscle" wrote in message oups.com... Thank you for the reply. I like your point about the fact that a lot of the published articles are probably done by fire departments, etc. But taking the example of the Ideal wire nut ... who do I believe. The information presented he www.inspect-ny.com/aluminum/twistcpsc.htm www.inspect-ny.com/aluminum/ideal65.htm www.inspect-ny.com/aluminum/i65debat.htm Or individuals like yourself and others who've never had issues with these connectors in their own homes? Hence my dilema ... Also, as a side point ... what do you consider "properly terminated"? Using AL approved outlets and switches, pigtailing, etc.? Thanks, Harry In addition to using properly labeled fixtures, the main thing you need to use is an antioxidant on the aluminum where it is joined to any other wire or terminal. The AL wire should also be scraped or sanded to remove oxidation before making a connection. (I think this is in the NEC) The failure mode of AL wiring is a build up of aluminum oxide (equivalent of rust) inside the terminal contacts. This causes a rise in resistance of the junction which will experience heating when current is flowed through it. With enough resistance and current, sufficient heat can build up to ignite nearby sources. Placing a paste like anti oxidant on freshly stripped and sanded AL wire will prevent the oxidation from occurring in the first place and ensure a low resistance connection. The terminals on CU/AL rated fixtures are more thermally compatible with the AL so that it does not come loose (due to thermal expansion) which is another cause for increased resistance and eventually heat. With lamps turned on or something plugged into a receptacle, if you feel any warmth coming from behind the wall plate, you should do something about those immediately. |
#12
|
|||
|
|||
"PipeDown" wrote in message news "Harry Muscle" wrote in message oups.com... Thank you for the reply. I like your point about the fact that a lot of the published articles are probably done by fire departments, etc. But taking the example of the Ideal wire nut ... who do I believe. The information presented he www.inspect-ny.com/aluminum/twistcpsc.htm www.inspect-ny.com/aluminum/ideal65.htm www.inspect-ny.com/aluminum/i65debat.htm Or individuals like yourself and others who've never had issues with these connectors in their own homes? Hence my dilema ... Also, as a side point ... what do you consider "properly terminated"? Using AL approved outlets and switches, pigtailing, etc.? Thanks, Harry In addition to using properly labeled fixtures, the main thing you need to use is an antioxidant on the aluminum where it is joined to any other wire or terminal. The AL wire should also be scraped or sanded to remove oxidation before making a connection. (I think this is in the NEC) The failure mode of AL wiring is a build up of aluminum oxide (equivalent of rust) inside the terminal contacts. This causes a rise in resistance of the junction which will experience heating when current is flowed through it. With enough resistance and current, sufficient heat can build up to ignite nearby sources. Placing a paste like anti oxidant on freshly stripped and sanded AL wire will prevent the oxidation from occurring in the first place and ensure a low resistance connection. The terminals on CU/AL rated fixtures are more thermally compatible with the AL so that it does not come loose (due to thermal expansion) which is another cause for increased resistance and eventually heat. With lamps turned on or something plugged into a receptacle, if you feel any warmth coming from behind the wall plate, you should do something about those immediately. No offense intended. Sanding a bare new conductor went out 20 years ago along with tape built up stress cones. If there is oxidation on the wire when terminating after you cut back the insulation, testing is in order in my mind. There could be more issues involved. Anti oxidant is a good thought. The local utility and I have used axle grease in a pinch. I learned that from them not the other way around. All your trying to do is prevent oxidation after the connection is made. I will and do use anti oxidant on terminations and splices. There were switches and outlets that when the side screws were used no anti ox was needed. I have not tried to buy them in ages cause I do not do that kind of work any more. I do know that going to the box stores and trying to find an device for AL is going to be next to impossible. At least in the box stores I have been in lately. Pigtailing out in copper is/was an acceptable method. Ask some pros in you local area to see what they do. |
#13
|
|||
|
|||
SQLit posted for all of us...
I don't top post - see either inline or at bottom. Sanding a bare new conductor went out 20 years ago along with tape built up stress cones. tape build up stress cones?? What are they? Googled but no results... -- Tekkie |
#14
|
|||
|
|||
"Harry Muscle" wrote in message oups.com... Thank you for the reply. I like your point about the fact that a lot of the published articles are probably done by fire departments, etc. But taking the example of the Ideal wire nut ... who do I believe. The information presented he www.inspect-ny.com/aluminum/twistcpsc.htm www.inspect-ny.com/aluminum/ideal65.htm www.inspect-ny.com/aluminum/i65debat.htm Or individuals like yourself and others who've never had issues with these connectors in their own homes? Hence my dilema ... Also, as a side point ... what do you consider "properly terminated"? Using AL approved outlets and switches, pigtailing, etc.? Thanks, Harry Take the high road, use copper. a roll of copper romex isnt that expensive. skip the hair splitting. Phil Scott |
#15
|
|||
|
|||
SQLit:
SQLit wrote: [...] I have been installing AL for more than 30 years. There is nothing wrong with the wire. The problems come from the installers and the terminations. If properly terminated there will be no more problems with AL than copper. I do not know of any utilities that use copper any more. All of the long lines and distribution lines in the West are primarily AL. If they were not some maroon would steal them. Which has happened in the old days, 1960-70's. All of that wire was replaced with AL. [...] Ideal makes a wire nut for AL-CU connections. About $2 ea at the box stores. Devices should be listed AL-CU and they are harder and harder to find. The AL metal its a superior conductor, and it is durable and easy to work and install. I understand that oxidation of the Al metal surfaces at the connections are the main problem. AL oxide has a high dielectric strength, meaning that it is poor conductor of electricity. In a simple connection, and over the span of a few years, the AL oxide forms on the exposed surfaces. The AL to AL contact area gets smaller. The electrical resistance at the contact area is increased. Heating is a function of current and resistance. The contact area get hot, and if the resistance is high enough slight melting could occur. the contact area or the cross sectional area of the wires may get smaller, and the resistance, and hence the heating, increases. The connection melts down and fails. CU oxide does not have as high a dielectric strength, and while the same process can occur the amount of heat produced may be less. I read that a coating can be applied to the finished connection of AL-AL or AL-CU metals that prevents oxidation over a long period of time. That, I think, is used in marine or shore environments. What is that coating? Crimp type clamped wire connections may provide great enough contact surface area and no access to O2 that the contact keeps a very low resistance that is lower than the wire itself for the life of the connection. AL wiring is low in cost, and is an efficient conductor. If oxidation is allowed to occur in either AL or CU connections, especially those that are not made with a sufficient surface contact area, and that are not tight, heating and sputtering can occur. I had a window air conditioning unit that was connected to two 3-wire extension cables. The copper contacts of the power cable had green oxidation, and after the power went on the cable outer ends were warm. Later in the day the cable to cable connection exploded in a flash of light and smoke. The circuit breaker opened. I am highly suspicious of cheap power extension cables that have the wires and metal bits molded into a low melting temperature rubbery plastic cable end with no other wire separators or electrical insulation. Corrosion free connectors may save electricity. Ralph Hertle |
#16
|
|||
|
|||
According to Ralph Hertle :
The AL metal its a superior conductor, and it is durable and easy to work and install. AL is a poorer conductor. Simple physics. Look it up. That's why it has to be a guage larger than copper for the same ampacity. It's reasonably durable, but not only is it stiffer (both because it is stiffer than copper to begin with, and because it has to be a gauge larger for the ampacity), it's more brittle. Hence, more difficult to work with than copper for the same ampacity, and more likely to get work-hardened and crack if not handled properly. And finally, due to its dialectric and "cold creep" properties, under identical conditions, it will deteriorate faster than copper. As such, aluminum is far more sensitive to sloppy workmanship, codes _require_ anti-oxidant grease (not necessary for copper), and most municipalities have banned the use of aluminum in residential wiring. Certainly, for power distribution (60A and up), its price advantage is enormous, so you do what you need to to make it safe. But in general residential wiring, these days its a very bad idea. And illegal in many places. I've been working with wiring for a very long time. The only connections I've ever seen burn out (aside from ones physically damaged, exposed to water, or due to unbelievably bad workmanship) have been aluminum. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#17
|
|||
|
|||
You made some good points on the differences between Al and Cu. Just
to further clarify, Cu has both and electrical and thermal conductivity that is nearly 65% greater than that of Al. Not only does conduct electrons better, Cu ability to dissipate heat is far greater than that of aluminum. Cu does oxide at room temperature, but rather slowly. Further, Cu oxide (CuO) does not form a tough coherent film. On the other hand Al is one of the most powerful reducing agents known to man (check out the thermite reaction http://en.wikipedia.org/wiki/Thermite). Any aluminum surface oxidizes almost immediately and as the oxide layer grows conductivity drops exponentially (this is why aluminum is so difficult to solder). Both metals are prone to work hardening (if bend it repeatedly it gets stiffer and then breaks). On the down size Cu is more expensive and 3 times more dense than Al, but weight matters little in a home. If sized properly to compensate for current load as well the use of dielectric greases, Al is a fine choice. On the other hand if done poorly, the joints could easily heat up as the aluminum oxide grows and potentially cause a fire. Without a doubt aluminum makes an excellent choice for high tension power lines, however, in the home I would prefer copper. This doesnt make aluminum unsafe, its just a preference. |
#18
|
|||
|
|||
Ralph Hertle wrote:
The AL metal its a superior conductor, and it is durable and easy to work and install. GOOD conductor? Yes, if properly installed. Durable, etc.? Same answer. But silver and copper are better conductors of electricity. -- If John McCain gets the 2008 Republican Presidential nomination, my vote for President will be a write-in for Jiang Zemin. |
#19
|
|||
|
|||
SQLit wrote:
Your home and mine (also built in 1971) have lasted this long. Chances are they will last a lot more. This is my 3 home of this vintage. Do you know anyone with a 1000 volt meggar? You will need to unplug EVERYTHING for the test. The meggar can tell you if there is an insulation problem and to a point loose connections. A megger only finds damaged insulation where there is a carbon path to ground (or line-to-line). I think it would find a small percentage of actual aluminum problems and no loose connections. Disconnect GFCIs if you use one. Bud-- |
#20
|
|||
|
|||
Bud wrote:
SQLit wrote: Your home and mine (also built in 1971) have lasted this long. Chances are they will last a lot more. This is my 3 home of this vintage. Do you know anyone with a 1000 volt meggar? You will need to unplug EVERYTHING for the test. The meggar can tell you if there is an insulation problem and to a point loose connections. A megger only finds damaged insulation where there is a carbon path to ground (or line-to-line). I think it would find a small percentage of actual aluminum problems and no loose connections. Disconnect GFCIs if you use one. Bud-- If the problem is due to a loose connection or oxidation induced high resistance, then a multimeter will certainly detect that on the resistance measurement function. Matt |
#21
|
|||
|
|||
Matt Whiting wrote:
Bud wrote: SQLit wrote: Your home and mine (also built in 1971) have lasted this long. Chances are they will last a lot more. This is my 3 home of this vintage. Do you know anyone with a 1000 volt meggar? You will need to unplug EVERYTHING for the test. The meggar can tell you if there is an insulation problem and to a point loose connections. A megger only finds damaged insulation where there is a carbon path to ground (or line-to-line). I think it would find a small percentage of actual aluminum problems and no loose connections. Disconnect GFCIs if you use one. Bud-- If the problem is due to a loose connection or oxidation induced high resistance, then a multimeter will certainly detect that on the resistance measurement function. (A multimeter is different from a megger.) I don't think it is too practical to measure the junction resistance. How do you connect to the wire that is on at least one side. Tests have shown that wirenuts fail by the contact made not wire-to-wire because of oxidation but through the steel spring. I remember the resistance being about 2 ohms, not much. Not enough to dim lights, no flicker. But the steel spring becomes a heating element that destroys insulation and can ultimately cause a fire. 2 ohms may be hard to find with a multimeter. Bud-- |
#22
|
|||
|
|||
Bud wrote:
Matt Whiting wrote: Bud wrote: SQLit wrote: Your home and mine (also built in 1971) have lasted this long. Chances are they will last a lot more. This is my 3 home of this vintage. Do you know anyone with a 1000 volt meggar? You will need to unplug EVERYTHING for the test. The meggar can tell you if there is an insulation problem and to a point loose connections. A megger only finds damaged insulation where there is a carbon path to ground (or line-to-line). I think it would find a small percentage of actual aluminum problems and no loose connections. Disconnect GFCIs if you use one. Bud-- If the problem is due to a loose connection or oxidation induced high resistance, then a multimeter will certainly detect that on the resistance measurement function. (A multimeter is different from a megger.) I don't think it is too practical to measure the junction resistance. How do you connect to the wire that is on at least one side. Tests have shown that wirenuts fail by the contact made not wire-to-wire because of oxidation but through the steel spring. I remember the resistance being about 2 ohms, correction -this should be a drop of 2 volts at a significant current; if hte current was 10A the resistance would be 0.2 ohms not much. Not enough to dim lights, no flicker. But the steel spring becomes a heating element that destroys insulation and can ultimately cause a fire. 0.2 ohms may be hard to find with a multimeter. Bud-- |
#23
|
|||
|
|||
Bud wrote:
Matt Whiting wrote: Bud wrote: SQLit wrote: Your home and mine (also built in 1971) have lasted this long. Chances are they will last a lot more. This is my 3 home of this vintage. Do you know anyone with a 1000 volt meggar? You will need to unplug EVERYTHING for the test. The meggar can tell you if there is an insulation problem and to a point loose connections. A megger only finds damaged insulation where there is a carbon path to ground (or line-to-line). I think it would find a small percentage of actual aluminum problems and no loose connections. Disconnect GFCIs if you use one. Bud-- If the problem is due to a loose connection or oxidation induced high resistance, then a multimeter will certainly detect that on the resistance measurement function. (A multimeter is different from a megger.) I don't think it is too practical to measure the junction resistance. How do you connect to the wire that is on at least one side. Tests have shown that wirenuts fail by the contact made not wire-to-wire because of oxidation but through the steel spring. I remember the resistance being about 2 ohms, not much. Not enough to dim lights, no flicker. But the steel spring becomes a heating element that destroys insulation and can ultimately cause a fire. 2 ohms may be hard to find with a multimeter. How is the steel spring any different for Al wire than for Cu wire? It's heating is a function of the current through it or what it absorbs from the wire, not a function of the type of metal connected to it. Heat is generated by ohmic resistance, and that comes from corrosion between the Aluminum wires or the wires and the wire nut spring, not the spring itself. Matt |
#24
|
|||
|
|||
Does anyone know if using (and regularly testing) AFCI (Arc Fault
Circuit Interrupers) increases reliability aluminium wiring to that of copper wiring when the current connection mechanisms are used? ----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==---- http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups ----= East and West-Coast Server Farms - Total Privacy via Encryption =---- |
#25
|
|||
|
|||
Newsgroups: misc.consumers.house
From: Mark Fineman Date: Wed, 10 Aug 2005 21:30:08 -0400 Local: Wed, Aug 10 2005 9:30 pm Subject: Info to backup safety of aluminum wiring? Does anyone know if using (and regularly testing) AFCI (Arc Fault Circuit Interrupers) increases reliability aluminium wiring to that of copper wiring when the current connection mechanisms are used? *** A very good question. I'd love to know the answer too. Thanks, Harry |
#26
|
|||
|
|||
Harry Muscle wrote:
I've moved into a house build in 1971 which is wired mainly with aluminum wiring. I've read a handful of published information that states that aluminum wiring (or more correctly, the connections made with aluminum wiring) do in fact create a fire hazard greater than copper wire. I also know that a lot of people state that aluminum wiring does not pose any greater risk than copper if done properly. What I'm interested in is what is "done properly" and have there been tests done on such "proper" wiring methods to prove that they do in fact pose no increased fire hazard? So in other words, what I'm looking for is published (on paper, internet, etc.) information from reputable sources that would refute the claims made by the information that I've already read making aluminum out to be a fire hazard. A lot of the information I've read so far can be found at www.inspect-ny.com/aluminum.htm Thanks for the input, Harry 1971 was a particularly bad year. Aluminum wiring is just fine for feeders, service entrance conductors, and other large capacity circuits (generally, 30A and larger). The biggest problem was with 15A devices sold until about 1972 -- it was impossible to make a proper connection with aluminum wire that would not oxidize and eventually fail. Aluminum wiring to an electric stove, clothes drier, central A/C, water heater, or subpanel is probably OK (the terminals will be listed something like "CU-AL" or "AL7CU") There are new (expensive) replacement devices that are listed for use with copper or aluminum wire that are marked "CO-ALR" (if I recall correctly) that can be used on aluminum 15A branch circuits without needing copper or copper-clad pigtails. I believe the CO-ALR devices is a better retrofit than adding a copper pigtail unless you get special crimp connectors made especially for joining small aluminum-to-copper conductors. I would not live in a house with 15A aluminum branch circuits unless *every* connection had been inspected and upgraded as necessary. I would rip the "easy" ones out completely and replace with copper. Best regards, Bob (not an electrician, just opinionated :-) |
#27
|
|||
|
|||
According to zxcvbob :
1971 was a particularly bad year. Aluminum wiring is just fine for feeders, service entrance conductors, and other large capacity circuits (generally, 30A and larger). The biggest problem was with 15A devices sold until about 1972 -- it was impossible to make a proper connection with aluminum wire that would not oxidize and eventually fail. If it was done _correctly_, Al wiring has always been safe. Cu/AL rated connectors/devices have been around as long as Al wire has. The problem mostly being craftsmen who didn't follow the rules, and Al being less forgiving of poor workmanship. Aluminum wiring to an electric stove, clothes drier, central A/C, water heater, or subpanel is probably OK (the terminals will be listed something like "CU-AL" or "AL7CU") BTW: "CU-AL" designations are largely obsolete, electrical standards now primarily call for CO-ALR. Considered better than CU-AL, but CU-AL is still okay I believe the CO-ALR devices is a better retrofit than adding a copper pigtail unless you get special crimp connectors made especially for joining small aluminum-to-copper conductors. Canada has always accepted CO-ALR wirenuts alone (without anti-oxidant grease) for routine 15A circuits. But the wirenuts are becoming harder and harder to find and are quite expensive (compared to ordinary ones). [Larger Al connections require appropriatedly rated terminal connectors/ clamp devices, and anti-oxidant grease like in the US.] US code appears to have been fluctuating rather a lot in regards to copper pigtailing. At one point at least, the ONLY legal way to pigtail Al to copper was with a very specialized crimp connector (~$5-10 _each_) and an expensive crimping tool ($500). IIRC, the "system" was manufactured by "AMP", and they wouldn't sell you the stuff unless you took a course on how to use it. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#28
|
|||
|
|||
OK, what I don't understand then is why a testing agency is able to
proof that for example a wirenut approved for aluminum can fail when installed properly and under normal conditions. If this wire nut is part of the "proper" methods involved in installing aluminum wiring, and when done properly is supposed to be completely safe, then why are they able to prove that it's unsafe? I'm specifically refering to the information on the Ideal wire nuts presented here www.inspect-ny.com/aluminum.htm (about half way down the page). Thanks, Harry *** Chris Lewis Aug 10, 9:54 am According to zxcvbob : 1971 was a particularly bad year. Aluminum wiring is just fine for feeders, service entrance conductors, and other large capacity circuits (generally, 30A and larger). The biggest problem was with 15A devices sold until about 1972 -- it was impossible to make a proper connection with aluminum wire that would not oxidize and eventually fail. If it was done _correctly_, Al wiring has always been safe. Cu/AL rated connectors/devices have been around as long as Al wire has. The problem mostly being craftsmen who didn't follow the rules, and Al being less forgiving of poor workmanship. Aluminum wiring to an electric stove, clothes drier, central A/C, water heater, or subpanel is probably OK (the terminals will be listed something like "CU-AL" or "AL7CU") BTW: "CU-AL" designations are largely obsolete, electrical standards now primarily call for CO-ALR. Considered better than CU-AL, but CU-AL is still okay I believe the CO-ALR devices is a better retrofit than adding a copper pigtail unless you get special crimp connectors made especially for joining small aluminum-to-copper conductors. Canada has always accepted CO-ALR wirenuts alone (without anti-oxidant grease) for routine 15A circuits. But the wirenuts are becoming harder and harder to find and are quite expensive (compared to ordinary ones). [Larger Al connections require appropriatedly rated terminal connectors/ clamp devices, and anti-oxidant grease like in the US.] US code appears to have been fluctuating rather a lot in regards to copper pigtailing. At one point at least, the ONLY legal way to pigtail Al to copper was with a very specialized crimp connector (~$5-10 _each_) and an expensive crimping tool ($500). IIRC, the "system" was manufactured by "AMP", and they wouldn't sell you the stuff unless you took a course on how to use it. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#29
|
|||
|
|||
Harry Muscle wrote:
OK, what I don't understand then is why a testing agency is able to proof that for example a wirenut approved for aluminum can fail when installed properly and under normal conditions. If this wire nut is part of the "proper" methods involved in installing aluminum wiring, and when done properly is supposed to be completely safe, then why are they able to prove that it's unsafe? I'm specifically refering to the information on the Ideal wire nuts presented here www.inspect-ny.com/aluminum.htm (about half way down the page). 1. NOTHING is "completely" safe. URL listing means only that the components passed the specific tests as certified. How valid those tests are under "field" as opposed to "laboratory" conditions is only one of the many issues involved. 2. There's an assumption that the cases of failure noted are comparable installations to those of the UL tests. That may or may not be the case. To answer such a general question would take a great deal of research into the bases for the tests and the conditions down to almost a sample-by-sample basis. From a quick glance at the site you reference, I'm not sure exactly how objective it is--it seems at first blush to be dedicated to the proposition that Al wiring is unsafe. Not saying it's not, just that to confirm/deny any of the alllegations there would take a significant amount of effort/time I don't have. |
#30
|
|||
|
|||
I don't know if this is an aluminum thing or not, but many electric service
connections are aluminum. These done properly are applied with aluminum wire goop and then the connections are torqued to main panel manufacturer's specifications. Yet it is not uncommon for these connections to become loose and need to be re-torqued. The question is: Does this occur more so with aluminum main service wiring than with copper main service wiring? |
#31
|
|||
|
|||
Harry Muscle wrote:
OK, what I don't understand then is why a testing agency is able to proof that for example a wirenut approved for aluminum can fail when installed properly and under normal conditions. If this wire nut is part of the "proper" methods involved in installing aluminum wiring, and when done properly is supposed to be completely safe, then why are they able to prove that it's unsafe? I'm specifically refering to the information on the Ideal wire nuts presented here www.inspect-ny.com/aluminum.htm (about half way down the page). I know now what bugged me about the site...wonder if it's a front for or being run in conjunction with a lawyer or firm looking for ammunition for class liability lawsuit... |
#32
|
|||
|
|||
Duane Bozarth wrote:
Harry Muscle wrote: OK, what I don't understand then is why a testing agency is able to proof that for example a wirenut approved for aluminum can fail when installed properly and under normal conditions. If this wire nut is part of the "proper" methods involved in installing aluminum wiring, and when done properly is supposed to be completely safe, then why are they able to prove that it's unsafe? I'm specifically refering to the information on the Ideal wire nuts presented here www.inspect-ny.com/aluminum.htm (about half way down the page). I know now what bugged me about the site...wonder if it's a front for or being run in conjunction with a lawyer or firm looking for ammunition for class liability lawsuit... The site is run by a home inspector. His interest is that home inspectors encounter conditions that may be a hazard and should be reported in an inspection report. The site collects information and has web links on a number of issues. On aluminum a lot of the information comes from the US Consumer Product Safety Commision and Jesse Aronstein, PH.D., P.E., who was a vice president at Wright-Malta Corp. Wright-Malta is a test laboratory that did extensive testing on aluminum wiring and associated devices. (The also did some testing on FPE circuit breakers for the CSPC.) I see no evidence that the inspect-ny web site is other than an honest attept to furnish unbiased information. Bud-- |
#33
|
|||
|
|||
According to Harry Muscle :
OK, what I don't understand then is why a testing agency is able to proof that for example a wirenut approved for aluminum can fail when installed properly and under normal conditions. If this wire nut is part of the "proper" methods involved in installing aluminum wiring, and when done properly is supposed to be completely safe, then why are they able to prove that it's unsafe? I'm specifically refering to the information on the Ideal wire nuts presented here www.inspect-ny.com/aluminum.htm (about half way down the page). People should probably remember that once someone has expressed an opinion in "their field", they tend to vociferously defend it, often well after it's been proven wrong. Notice the study on Ideal wirenuts was done by the author of the site. I'm frankly a bit confused by the stuff about the Ideal wirenut. It's being summarized as "The Ideal #65 wirenut doesn't meet UL test XYZ" Yet, the _only_ "real" response from UL is to say "You seem to be asking us to add more tests to UL XYZ". In otherwords, UL is implying that the tests do _not_ invalidate the UL test, the author of the test is doing something _different_. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#34
|
|||
|
|||
I don't think the author of this page is the same guy as who did the
tests ... unless I'm not seeing something you're seeing. Thanks, Harry |
#35
|
|||
|
|||
Harry Muscle wrote:
OK, what I don't understand then is why a testing agency is able to proof that for example a wirenut approved for aluminum can fail when installed properly and under normal conditions. If this wire nut is part of the "proper" methods involved in installing aluminum wiring, and when done properly is supposed to be completely safe, then why are they able to prove that it's unsafe? I'm specifically refering to the information on the Ideal wire nuts presented here www.inspect-ny.com/aluminum.htm (about half way down the page). Thanks, Harry The argument by the US Comsumer Product Safety Council was that the test standard from UL was not adequate to test aluminum. Issues included using 'current' aluminum wire instead of wire that was used before 1971. Also that laboratory tests showed the wire nut (Ideal #65 Twister) subject to failure (with the plastic body and the internal antioxidant supporting fire). Part of the significance of this is that the Ideal wire nut was probably the only wire nut listed by UL for use with aluminum and copper. (Ideal has said the wire nut was not intended for use in pigtailing retrofit application, but was intended for such applications as connecting lighting fixtures and ceiling fans.) One of the sites linked from inspect-ny is http://www.inspect-ny.com/aluminum/alreduce.htm ************************************************** ******************* IF YOU HAVE ALUMINUM WIRING I STRONGLY SUGGENT YOU LOOK AT THIS SITE. ************************************************** ******************* It is a paper writen by Jesse Aronstein P.E. who was a vice president at Wright-Malta Corp. Wright Malta is a test laboratory did a lot of testing of aluminum wire and associated devices for the CSPC and others. The paper includes: - aluminum wiring systems, including those installed after UL changed the standards for wire and devices about 1971, are potential hazards - information on COPALUM crimp connections referred to in other posts (these probably can only be made by a electrician trained by the manufacturer) - what the problem is with wire nuts - very specific information on using wirenuts to make connections to a copper pigtail to connect to a device. - existing wirenuts in an aluminum should be replaced - very specific information on connections of aluminum wire to switches and receptacles - information on connecting aluminum wire to circuit breakers Also other very useful information. It should be emphasized that this information is based on tests, not conjecture. The paper was writen in 2000. In information on FPE breakers, inspect-ny says that the CPSC tried to regulate aluminum wire systems but was sued by the aluminum industry. The courts found that aluminum wiring systems were not consumer products and not subject to CPSC regulation (consumers do not buy significant aluminum system products). --------------------- Does anyone know what wirenuts, if any, are listed for aluminum and copper? Bud- |
#36
|
|||
|
|||
"Harry Muscle" wrote in message
ups.com... I've moved into a house build in 1971 which is wired mainly with aluminum wiring. I've read a handful of published information that states that aluminum wiring (or more correctly, the connections made with aluminum wiring) do in fact create a fire hazard greater than copper wire. I also know that a lot of people state that aluminum wiring does not pose any greater risk than copper if done properly. What I'm interested in is what is "done properly" and have there been tests done on such "proper" wiring methods to prove that they do in fact pose no increased fire hazard? So in other words, what I'm looking for is published (on paper, internet, etc.) information from reputable sources that would refute the claims made by the information that I've already read making aluminum out to be a fire hazard. A lot of the information I've read so far can be found at www.inspect-ny.com/aluminum.htm Thanks for the input, Harry Sounds like you're trying to substantiate denial. Too many horror stories of houses burning to the ground due to electrical wiring defects. If you're trying to make a house addition or electrical mod, there's connectors for AL-CU. Check local building code before using. |
#37
|
|||
|
|||
According to Harry Muscle :
I've moved into a house build in 1971 which is wired mainly with aluminum wiring. I've read a handful of published information that states that aluminum wiring (or more correctly, the connections made with aluminum wiring) do in fact create a fire hazard greater than copper wire. I also know that a lot of people state that aluminum wiring does not pose any greater risk than copper if done properly. What I'm interested in is what is "done properly" and have there been tests done on such "proper" wiring methods to prove that they do in fact pose no increased fire hazard? So in other words, what I'm looking for is published (on paper, internet, etc.) information from reputable sources that would refute the claims made by the information that I've already read making aluminum out to be a fire hazard. A lot of the information I've read so far can be found at www.inspect-ny.com/aluminum.htm What you're going to find out is that everybody agrees that Al done improperly is a high risk. Then find that there is considerable disagreement over whether Al "done properly" represents enough _more_ of a risk over copper to be concerned about. So you're not going to find exactly what you want in terms of "proof". As for "done properly": This means, from code: - devices with the old "CU-AL" or the newer "CO-ALR" ratings. (primarily: outlets, switches and breaker terminals) - copper pigtails to devices that aren't. - Al-compatible wirenuts. COPALUM connectors if necessary for Al to Cu connections. - Each connection to a device (ie: outlets, switches, and some breakers) MUST be via a screw terminal, with the wire wrapped between 3/4 and 1 full turn. In other words, properly formed loops. NEVER use push in terminals. Follow connection requirements on breakers to the letter. - wire must not be knicked, and minimally handled to avoid work hardening. - where appropriate the connections should have anti-oxidant grease. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#38
|
|||
|
|||
OK, I think Arnold summarized things pretty well so far:
*** What you're going to find out is that everybody agrees that Al done improperly is a high risk. Then find that there is considerable disagreement over whether Al "done properly" represents enough _more_ of a risk over copper to be concerned about. So you're not going to find exactly what you want in terms of "proof". *** So in other words, AL wiring can be made safer, but even done properly it's very possible that it will never be as safe as copper .... with the possible exception of using the COPALUM tool ... no one seems to have ever been able to show that a connection made with the COPALUM tool can fail under normal conditions ... which would coincide with what SQLit said about hydrolic pressed connections never failing, since the COPALUM is basically that, a hydrolic crimping tool. Thanks for everyone's input, Harry |
#39
|
|||
|
|||
Oops, that wasn't Arnold that said that, it was Chris Lewis ... sorry
about that. Harry |
#40
|
|||
|
|||
Chris Lewis wrote: As for "done properly": This means, from code: - devices with the old "CU-AL" or the newer "CO-ALR" ratings. (primarily: outlets, switches and breaker terminals) - copper pigtails to devices that aren't. - Al-compatible wirenuts. COPALUM connectors if necessary for Al to Cu connections. - Each connection to a device (ie: outlets, switches, and some breakers) MUST be via a screw terminal, with the wire wrapped between 3/4 and 1 full turn. In other words, properly formed loops. NEVER use push in terminals. Follow connection requirements on breakers to the letter. - wire must not be knicked, and minimally handled to avoid work hardening. - where appropriate the connections should have anti-oxidant grease. Is there any input on the life of anti-oxidant greased connections? In other words, will the grease dry out over time and cease it's anti-oxidation properties? Having a AL wired house and not trusting mass produced housing workmanship, I went through the entire house, removed all connections, cleaned them, used anti-oxidant, and insured tight connections when I reconnected. But that was 20 years ago. I've never had any problems, but I'm wondering if going through and doing it again is necessary, or maybe even a bad idea. Bob S. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
First Aluminum Anodizing attempts (long w/ pictures) | Metalworking | |||
aluminum wiring | Home Repair | |||
240 volt wiring | Home Repair | |||
Corrosion of Aluminum wiring | UK diy | |||
aluminum wiring | Home Repair |