Home |
Search |
Today's Posts |
|
#1
|
|||
|
|||
Can't connect power, GFCI weird?
I have some new wiring runs and was doing some checking before
connecting to mains when I discovered that a 9V battery was pushing 25 or so micro-amps down a circuit that was supposed to be open, as nothing was plugged into the GFCI outlets and and lamp sockets were also empty. This was causing a reduction in voltage due to the battery being loaded. Looking further, I found that each GFCI (there are 3 in parallel in this circuit) had continuity from live to neutral and showed a resistance of about 360 Ohms on a DMM, causing about 120 Ohms at the end that is supposed to go into the breaker panel. The GFCIs are made by Pass & Seymour (also says Legrand on the box). Their website doesn't address this issue. These are their "premium" line and have an LED on the front. A Leviton GFCI without any LED shows an open between the live and neutral. I don't know if all the GCFIs I bought can be simultaneously defective; or whether the LED or their current monitoring circuit us causing the continuity. 360 Ohms seems an awfully low resistance to show to 120V AC. Is the behavior under DC different than AC for a GFCI outlet? Seems pretty spooky... |
#2
|
|||
|
|||
Nexus7 wrote: I have some new wiring runs and was doing some checking before connecting to mains when I discovered that a 9V battery was pushing 25 or so micro-amps down a circuit that was supposed to be open, as nothing was plugged into the GFCI outlets and and lamp sockets were also empty. This was causing a reduction in voltage due to the battery being loaded. Looking further, I found that each GFCI (there are 3 in parallel in this circuit) had continuity from live to neutral and showed a resistance of about 360 Ohms on a DMM, causing about 120 Ohms at the end that is supposed to go into the breaker panel. The GFCIs are made by Pass & Seymour (also says Legrand on the box). Their website doesn't address this issue. These are their "premium" line and have an LED on the front. A Leviton GFCI without any LED shows an open between the live and neutral. I don't know if all the GCFIs I bought can be simultaneously defective; or whether the LED or their current monitoring circuit us causing the continuity. 360 Ohms seems an awfully low resistance to show to 120V AC. Is the behavior under DC different than AC for a GFCI outlet? Seems pretty spooky... you might be seeing the load of the internal power supply inside the GFI that power the GFI itself. the DMM is probably seeing the completly discharged filter cap inside the GFI which will charge up and draw less current when you connect it to the AC line. Mark |
#3
|
|||
|
|||
I received a reply from Pass & Seymour's technical support. As part of
their "line load reversal test procedure," there is a small resistor in the GFCI that makes it trip when the outlet is first energized. I don't know if this procedure refers to what happens when first energized, or if it is some other test that is performed during the manufacturing process. In any event, I (bench) tested this on one outlet, then on the curcuit described. All 3 outlets duly tripped and the lights came on. After resetting, all are open between L and N, and the circuit is functioning correctly. Thanks to all those who replied. |
#4
|
|||
|
|||
Why do you have 3 GFCI outlets on the same circuit? Only the first one on
the line needed to be a GFCI and it would protect all the other outlets after it. You could also use a single GFCI breaker and then all the outlets on that branch circuit would be protected. At least that's the way mine work. I am glad to here you solved your problem though, I would have been surprised as well at the reading. They really should document that. Bill "Nexus7" wrote in message oups.com... I received a reply from Pass & Seymour's technical support. As part of their "line load reversal test procedure," there is a small resistor in the GFCI that makes it trip when the outlet is first energized. I don't know if this procedure refers to what happens when first energized, or if it is some other test that is performed during the manufacturing process. In any event, I (bench) tested this on one outlet, then on the curcuit described. All 3 outlets duly tripped and the lights came on. After resetting, all are open between L and N, and the circuit is functioning correctly. Thanks to all those who replied. |
#5
|
|||
|
|||
Bill Renfro wrote:
Why do you have 3 GFCI outlets on the same circuit? Only the first one on the line needed to be a GFCI and it would protect all the other outlets after it. You could also use a single GFCI breaker and then all the outlets on that branch circuit would be protected. At least that's the way mine work. I figured if I did it that way, diagnosing a trip or other condition would required knowing about the upstream outlet. I tried to minimize such "non-local" effects by just putting GFCIs anywhere that no major appliances would be plugged in. They were $10 on sale anywway. It's too bad I have keep some shared neutral circuits because of legacy issues, another instance where you have to know about the entire system to work on just part of it. |
#6
|
|||
|
|||
"Nexus7" writes:
Bill Renfro wrote: Why do you have 3 GFCI outlets on the same circuit? Only the first one on the line needed to be a GFCI and it would protect all the other outlets after it. You could also use a single GFCI breaker and then all the outlets on that branch circuit would be protected. At least that's the way mine work. I figured if I did it that way, diagnosing a trip or other condition would required knowing about the upstream outlet. I tried to minimize such "non-local" effects by just putting GFCIs anywhere that no major appliances would be plugged in. They were $10 on sale anywway. It's too bad I have keep some shared neutral circuits because of legacy issues, another instance where you have to know about the entire system to work on just part of it. So, now you will have some random combinatino of GFCIs tripping, rather than only one. Realize that there is no guarantee that only the GFCI at the affected outlet will trip! --- sam | Sci.Electronics.Repair FAQ Mirror: http://repairfaq.ece.drexel.edu/ Repair | Main Table of Contents: http://repairfaq.ece.drexel.edu/REPAIR/ +Lasers | Sam's Laser FAQ: http://repairfaq.ece.drexel.edu/sam/lasersam.htm | Mirror Sites: http://repairfaq.ece.drexel.edu/REPAIR/F_mirror.html Note: These links are hopefully temporary until we can sort out the excessive traffic on Repairfaq.org. Important: Anything sent to the email address in the message header above is ignored unless my full name is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Making custom power connectors | Metalworking | |||
eScrew OWNS YOU!!! | Metalworking | |||
eScrew | Woodworking | |||
Funny story about repair | Electronics Repair | |||
Generator FAQ | Metalworking |