Home Ownership (misc.consumers.house)

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Nexus7
 
Posts: n/a
Default Can't connect power, GFCI weird?

I have some new wiring runs and was doing some checking before
connecting to mains when I discovered that a 9V battery was pushing 25
or so micro-amps down a circuit that was supposed to be open, as
nothing was plugged into the GFCI outlets and and lamp sockets were
also empty. This was causing a reduction in voltage due to the battery
being loaded. Looking further, I found that each GFCI (there are 3 in
parallel in this circuit) had continuity from live to neutral and
showed a resistance of about 360 Ohms on a DMM, causing about 120 Ohms
at the end that is supposed to go into the breaker panel. The GFCIs are
made by Pass & Seymour (also says Legrand on the box). Their website
doesn't address this issue. These are their "premium" line and have an
LED on the front. A Leviton GFCI without any LED shows an open between
the live and neutral.

I don't know if all the GCFIs I bought can be simultaneously defective;
or whether the LED or their current monitoring circuit us causing the
continuity. 360 Ohms seems an awfully low resistance to show to 120V
AC. Is the behavior under DC different than AC for a GFCI outlet? Seems
pretty spooky...

  #2   Report Post  
Mark
 
Posts: n/a
Default


Nexus7 wrote:
I have some new wiring runs and was doing some checking before
connecting to mains when I discovered that a 9V battery was pushing

25
or so micro-amps down a circuit that was supposed to be open, as
nothing was plugged into the GFCI outlets and and lamp sockets were
also empty. This was causing a reduction in voltage due to the

battery
being loaded. Looking further, I found that each GFCI (there are 3 in
parallel in this circuit) had continuity from live to neutral and
showed a resistance of about 360 Ohms on a DMM, causing about 120

Ohms
at the end that is supposed to go into the breaker panel. The GFCIs

are
made by Pass & Seymour (also says Legrand on the box). Their website
doesn't address this issue. These are their "premium" line and have

an
LED on the front. A Leviton GFCI without any LED shows an open

between
the live and neutral.

I don't know if all the GCFIs I bought can be simultaneously

defective;
or whether the LED or their current monitoring circuit us causing the
continuity. 360 Ohms seems an awfully low resistance to show to 120V
AC. Is the behavior under DC different than AC for a GFCI outlet?

Seems
pretty spooky...



you might be seeing the load of the internal power supply inside the
GFI that power the GFI itself.

the DMM is probably seeing the completly discharged filter cap inside
the GFI which will charge up and draw less current when you connect it
to the AC line.

Mark

  #3   Report Post  
Nexus7
 
Posts: n/a
Default

I received a reply from Pass & Seymour's technical support. As part of
their "line load reversal test procedure," there is a small resistor in
the GFCI that makes it trip when the outlet is first energized. I don't
know if this procedure refers to what happens when first energized, or
if it is some other test that is performed during the manufacturing
process.

In any event, I (bench) tested this on one outlet, then on the curcuit
described. All 3 outlets duly tripped and the lights came on. After
resetting, all are open between L and N, and the circuit is functioning
correctly.

Thanks to all those who replied.

  #4   Report Post  
Bill Renfro
 
Posts: n/a
Default

Why do you have 3 GFCI outlets on the same circuit? Only the first one on
the line needed to be a GFCI and it would protect all the other outlets
after it. You could also use a single GFCI breaker and then all the outlets
on that branch circuit would be protected. At least that's the way mine
work.
I am glad to here you solved your problem though, I would have been
surprised as well at the reading. They really should document that.

Bill

"Nexus7" wrote in message
oups.com...
I received a reply from Pass & Seymour's technical support. As part of
their "line load reversal test procedure," there is a small resistor in
the GFCI that makes it trip when the outlet is first energized. I don't
know if this procedure refers to what happens when first energized, or
if it is some other test that is performed during the manufacturing
process.

In any event, I (bench) tested this on one outlet, then on the curcuit
described. All 3 outlets duly tripped and the lights came on. After
resetting, all are open between L and N, and the circuit is functioning
correctly.

Thanks to all those who replied.



  #5   Report Post  
Nexus7
 
Posts: n/a
Default

Bill Renfro wrote:
Why do you have 3 GFCI outlets on the same circuit? Only the first

one on
the line needed to be a GFCI and it would protect all the other

outlets
after it. You could also use a single GFCI breaker and then all the

outlets
on that branch circuit would be protected. At least that's the way

mine
work.


I figured if I did it that way, diagnosing a trip or other condition
would required knowing about the upstream outlet. I tried to minimize
such "non-local" effects by just putting GFCIs anywhere that no major
appliances would be plugged in. They were $10 on sale anywway. It's
too bad I have keep some shared neutral circuits because of legacy
issues, another instance where you have to know about the entire system
to work on just part of it.



  #6   Report Post  
Sam Goldwasser
 
Posts: n/a
Default

"Nexus7" writes:

Bill Renfro wrote:
Why do you have 3 GFCI outlets on the same circuit? Only the first

one on
the line needed to be a GFCI and it would protect all the other

outlets
after it. You could also use a single GFCI breaker and then all the

outlets
on that branch circuit would be protected. At least that's the way

mine
work.


I figured if I did it that way, diagnosing a trip or other condition
would required knowing about the upstream outlet. I tried to minimize
such "non-local" effects by just putting GFCIs anywhere that no major
appliances would be plugged in. They were $10 on sale anywway. It's
too bad I have keep some shared neutral circuits because of legacy
issues, another instance where you have to know about the entire system
to work on just part of it.


So, now you will have some random combinatino of GFCIs tripping, rather
than only one.

Realize that there is no guarantee that only the GFCI at the affected
outlet will trip!

--- sam | Sci.Electronics.Repair FAQ Mirror: http://repairfaq.ece.drexel.edu/
Repair | Main Table of Contents: http://repairfaq.ece.drexel.edu/REPAIR/
+Lasers | Sam's Laser FAQ: http://repairfaq.ece.drexel.edu/sam/lasersam.htm
| Mirror Sites: http://repairfaq.ece.drexel.edu/REPAIR/F_mirror.html

Note: These links are hopefully temporary until we can sort out the excessive
traffic on Repairfaq.org.

Important: Anything sent to the email address in the message header above is
ignored unless my full name is included in the subject line. Or, you can
contact me via the Feedback Form in the FAQs.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Making custom power connectors Rick Metalworking 17 January 1st 05 06:15 PM
eScrew OWNS YOU!!! [email protected] Metalworking 7 December 22nd 04 09:47 PM
eScrew Dave Jackson Woodworking 1 December 21st 04 01:54 AM
Funny story about repair [email protected] Electronics Repair 0 December 20th 04 03:35 AM
Generator FAQ Gunner Metalworking 0 January 23rd 04 05:24 PM


All times are GMT +1. The time now is 08:54 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"