Thread
:
branch electric box question
View Single Post
#
9
Chris Lewis
Posts: n/a
According to :
On Tue, 23 Aug 2005 17:39:59 -0000,
(Chris
Lewis) wrote:
Does it not also say that _each_ conductor must be the same size, and
each capable of carrying the full breaker current?
[Our code does.]
Which basically means you can parallel conductors to reduce end-to-end
resistance (voltage drop), but NOT to increase circuit ampacity.
No you add the ampacity of paralleled conductors but bear in mind they
must be 1/0 or larger (about 10mm).
The reason you can parallel conductors is to use a size that is more
easily handled in large ampacity circuits.
As I mentioned, _not_ in our code.
You can only parallel conductors to decrease voltage drop. The individual
conductors must still be large enough to take the full ampacity.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
Reply With Quote