I am considering adding some run capacitors to my self starting RPC. I
am reading Jim Hanrahan's article at

http://www.metalwebnews.com/howto/ph-conv/ph-conv.html

and I am confused by something. I understand how self starting
RPCwould start with one cap between one leg 1 and leg 3 (the generated
one). That's how mine is wired. Jim makes a point that it works, but
makes unbalanced voltage.

But why would it start is capacitors are connected between 1-3 AND
2-3, like in this pictu

http://www.metalwebnews.com/howto/ph-conv/fig1.html

I cannot see how it would create assymmetric fields needed to spin up
the motor. Is that because capacitances across legs 1-3 are greater
than capacitance between leg 2-3?

I could try to use run caps at run time and start caps at start
time. In fact, I won a time delay relay for $9 on ebay yesterday, so I
could set the RPC to start on start cap (both caps between leg 1-3)
and then reconnect the same caps to become run caps, one between 1-3
and another between 2-3. Same TDR could, then, turn out output current
aftet time delay, allowing the RPC to spin up and switch to the run
mode.

As you can see, I am quite confused, but am willing to experiment. I
have 4 unused Furnas 75 A contactors that I can wire, with the time
delay relay, to do just about anything.

Idler: 10 HP

Capacitors: 92 mF each, 535 VAC rated, oil filled. I have 5 total, and
use 2 for the starting leg, so three are unused.

i

You are correct saying that it's because the capacitance between 1 + 3
is
higher than between 2 + 3.
My RPC, 10HP 440V 50Hz motor, has 40uF between 2 + 3, 60uF between 1 +
3 and
500uF switched by a start circuit between 1 + 3. The 500uF is a bit too
much, it starts very quickly (around 1/3 second) so I could probably
drop
that to around 200uF.

Thank you Martin.

I have five 92 mF caps total.

What I have now is 2 capacitors connected between leg 1 and 3.

It seems that about the only thing that I need, then, wire it as follows:

1. 1 cap (92 mF) between legs 1 and 2, permanently connected.

2. 1 cap (92 mF) between 1 and 3, permanently connected.

3. 2-3 more caps (180-270 mF) between legs 1 and 3, connected
at start time and switched off by the time delay relay (TDR),
say 4 seconds after startup.

4. (optional) add another contactor on output side that would only
switch output on when the TDR actuates and switches off the start
caps.

Theat would get me an RPC that is:

- properly balanced across the range of output HP
- starts quickly
- only turns on when balanced power is output and full rotational
speed is achieved, that is, when good quality 3 phase power is available.

Does it make sense?

i


With five equal value oil filled capacitors your options are fairly
limited but you can still finish up wth a perfectly good converter.

One thing to remember is that capacitors of this type have extremely
low internal series resistance (milliohms)- that's why you get a
sizable bang if you short circuit a charged one!
The same thing happens when you connect a charged capacitor to an
uncharged one - VERY high peak currents flow as the charge voltage
equalises on the two capacitors.


An excellent point.

The capacitors are not greatly bothered by this treatment but it's
very unkind to the switch contacts or relay contacts used to parallel
connect two capacitors if there is a substantial voltage difference at
the instant of connection.


Yep, makes full sense.

Now, based on common sense, unlike CONNECTING capacitors,
DISCONNECTING them should not produce any big sparks.

I have a plan for a start circuit with a separate contactor. The
sequence of events is as follows.

1. I turh the ON switch.
2. The contactor that connects starting caps engages.
3. When it engages, it actuates the SECOND contactor that supplies
primary 240V voltage to the electric motor.
4. Everything starts spinning.
5. After a few seconds, a time delay relay that I won on ebay today
(NO and NC), will open a pair of contacts and DISCONNECT the starting
caps.

I think that I know how to wire this properly so that all of this
happens, and yet everything shuts down when I turn the on/off switch
to off. I have a mental picture. Basically both contactors would have
a neutral wired directly to neutral, but the 110V line for signal
would go through the switch, then to 3rd poles of second contactor,
and to the 3rd pole of the first contactor but through a time delay
relay. then from the switched side of both contactors to the hot
switch terminal of the second contactor.

6. When the NO contacts on the time delay relay close, it would
actuate the third contactor that would allow power to be output.

Sorry if I am speaking in strange language, I am a computer
programmer. It should work, logically.

read on...

Brute force oversizing of the switching contacts can give reasonable
contact life but it's much neater to avoid the problem by using
separate start and run capacitors that are never parallel connected.
This is easily done with your capacitor collection.

Use three parallel connected as your start capacitor. Only in circuit
for the few seconds needed for the idler to run up to speed.


Right.

You now have a bit unbalanced but perfectly usable converter system.


right. it's much nicer to have something working and add stuff to it,
than build a "dream system" without testing to only realize that
something went amiss. That's how I do my programming too.

Ideally the load motor should not be switched in until the idler is up
to speed. However, if the load motor is initially running light, this
start capacitance is probably enough for a simultaneous idler and load
start.

Your START switching should be a changeover contact which EITHER
connects the start capacitor OR the run capacitor across L1 and L2.

For the run capacitor, try one capacitor or two capacitors series
connected to halve the effective value - whichever gives the best
voltage balance with full load on the load motor.


Looks like one run cap per side should be good, based on Jim
Hanrahan's writings. I'll see.

Do not place a capacitor across L2 L3. With the values you have
available this would do more harm than good.


Hm, why is that so?

Anyway, my main question is: if I do all this (as I outlined in steps
1-6), will I get a Mercedes Benz of phase converters? Or am I wasting
my time for load up to and under 5 HP?

i


I

It would be rude for me to agree that you'd be wasting your time by
sophisticating this RPC. I can tell you that nothing you are likely to
*ever* use in your house will be able to operate any better because of
*anything you do beyond just spinning up that 10 HP idler.

Jerry