View Single Post
  #6   Report Post  
Z
 
Posts: n/a
Default Earth bonding cable - minimum size?

In article , BigWallop
writes

"Lobster" wrote in message
. com...
Hi

Just completing a house wiring job, I've now got myself a tad confused
about what size of earth cable I should be using to bond the incoming
gas and water pipes to the main earth near the electric meter. I've
already used 10mm, but have got myself worried that this isn't big
enough and would rather get it right now than have the inspector tell
me to change it later (it's not a trivial task, as the gas and
electric meters are at opposite ends of the house!)

The electricity installation is new (and not yet connected to the CU),
and it's PME. The earth cable is completely protected mechanically
along its length... is there any other info needed to assess the
correct earth size? Or do I need to ask the supply company, ahich is
what the stuff at www.tlc-direct.co.uk seems to be suggesting?

Many thanks
David


From the mains service head you need to run 10 mm csa' green/yellow sheathed
conductors. On all the other supplementary bonding you would use 6 mm csa'
green/yellow sheathed conductors.


Though if you have a drum of 10 use 10 save ending up with 2 half drums
--
Z