You would only need #10 wire if the run was particularly long (i don't have
a table handy but it would be well over 100'). Normally a 15A circuit uses
#14 wire for typical length runs. If you are running a heavy load as is
typical in a kitchen you should be using #12 wire and 20A breakers.
Normally, 15A circuits are used only for lighting.

As for running more than one circuit in a conduit, it is fine as long as you
follow a couple of rules. First don't use romex or bundled cables in the
conduit as bundling reduces the allowed ampacity of the cable due to the
reduced ability to shed heat (besides you end up with extra ground
conductors and space taken up by the jacket which makes it harder to thread
into the conduit). Second note the insulation type and gage of all the
wires you want to run. Third look up the required conduit size to hold the
wires you want to run. If the branch is long or run in a hot space, you
will need to derate the wires and this usually means increasing the wire
gague and increasing the conduit diameter.

CodeCheck Electrical is a little spiral bound tablet with most of the really
important stuff. The wire size, derating information, length of branch and
conduit fill tables are all in there. Its a decent reference even if you
have a copy of the NEC it is easier to access.

You may not even need to use a conduit if the run is through sheltered areas
inaccessible to people. NM wire is easier and cheaper to run and you can
use 12-3 to run two 20A circuits at one time with one cable. If the wire is
in an exposed area you can't use NM but armored BX cable is needed and cost
is almost as much as conduit but easier to install.


PS, I'm a DIY not a pro.




"les" wrote in message ...
Hello...
I 'm considering running 3 new conduits from circuit braker panel to the
kitchen, but on second thought that's more piping than I really feel like
doing. But my question is if the codes frown on combining 3 separate
circuits within one conduit line.
I have no firm reason to see what hazard this would present assuming
wire guage and insulation are sound, but I need some expert voices to
set me on the correct path.
I plan to run 10 guage solid copper for 15 amp service.
I expect codes to vary regionally, so I'd like to hear the most stringent
opinions and perhaps any for Chicago area too.

Thanks