On Sun, 05 Jun 2005 00:03:03 GMT, wrote:

All,

Short story: On a US-standard 240/120 100 A service, I am seeing 8 to 9
volts difference between phases when a 120 V 1.3 kW microwave is
running. Is this excessive, or acceptable?

Long story:

For the past few mornings, the UPS (APC Smart-UPS 600) in my office has
been switching on to battery power for a few minutes, even when the
lights in the rest of the house hadn't flickered or gone out. I
finally put a meter (Metex ME-11 DMM) on the wall outlet supplying the
UPS while the UPS was running and found out it was probably tripping
on _over_voltage: the wall socket was delivering over 130 volts!

After a bit of experimentation, I discovered that the voltage went up
when the microwave in the kitchen was running, which is why it happened
in the mornings when the other half was making tea. The microwave is on
one of the 20 A kitchen circuits, while my office is on a 20 A
receptacle circuit with a couple of other rooms. It's a GE microwave,
about 10 years old, 120 V 1300 W per the nameplate. I also noticed that
the voltage rise was less pronounced when the central air conditioner was
running. The compressor is 240 V and is fused and breakered at 40 A.

Suspecting a loose neutral, I inspected the breaker panel. Nothing
looked out of place. I tried tightening all of the screws on the
neutral/ground bus bar. They all took a bit of tightening - less than
1/8 turn - but none were really badly loose. I made very sure that the
neutral coming in from the meter was tight at the bus bar. I have the
US-standard 240/120 service at, I believe, 100 amps, and a GE split-bus
panel. It is original to the house (1969), although the breakers have
all been replaced. To my knowledge, the kitchen circuits are two
separate 20 A circuits with their own NM cable, not split like a
Canadian kitchen circuit.

After I tightened the screws, I went around in the house and made sure
most things were turned off. There were still a few computers running,
but the TV, stereo, lights, etc were all off. The air conditioner was
also shut off. I measured the voltage between the neutral/ground bus
bar and each hot lug with the microwave off and then with the microwave
running, heating about 8 oz (230 mL) of water in a coffee cup. I then
turned the A/C on and tried again. Results...

A/C uWave left right l-r notes
off off 122.5 123.2 -0.7 run 1
off on 126.3 117.6 8.7

off off 121.9 121.3 0.6 run 2
off on 126.1 116.7 9.4

on off 119.6 123.3 -3.7
on on 123.7 118.5 5.2

I know that the two sides of the service will very rarely be in exact
balance, but the 8 to 9 V difference seems somewhat high. Is this
considered within reasonable bounds, or should I have the power company
out? Or should I chase the wiring in the house further? When I moved
into the house 5+ years ago, most of the receptacles were original and
back-wired. I changed all of them that are regularly used for new spec
grade side-wired receptacles.

Out of curiosity, I measured the voltage drop across each breaker. This
was with most of the loads shut off, so it may not be too useful, but I
found no breaker over 100 mV and most under 40 mV.

Let me know if you need more information. Thanks for your help!

Matt Roberds


I had a similar situation, but even greater voltage difference with
even smaller loads. Found it to be present at the panel. Sure looked
like a loose neutral in the 120/240 service. I was pretty certain it
was power company connections. Called the power company.
Fortunately I was an electrician in a previous career and left a note
on the meter telling sparky what I thought the problem was. I was
real scared that they would blow me off figuring I was some homeowner
nut case. Thank goodness when they came they found the neutral loose
in their meter section and fixed it pronto.