"Stefek Zaba" wrote in message
...
Dundonald wrote:


1. why didn't/doesn't the RCD trip before the fuse on the consumer unit


As Ellis said, an RCD only detects faults to earth, most obviously L to E.
If your wiring or lamp had an L-to-N short, that'll make the MCB pop, but
the RCD will be happy as Larry, since just as much current - in this case,
lots and oodles - is flowing out down the L as is coming back up the N.
2. any ideas what the likely cause of the problem is with the lamp -
just out of interest? Like I say I'll just get a replacement from B&Q
anyway but just curious.

As mentioned above, a fault making the L shorted to N. Either a fault in
the lamp, or - more likely, I'm afraid - you wired it up wrong (or ended
up with bare L and N conductors touching when you sqaushed them back in
place). The blackening of the brick, and the popping of the MCB, says you
had quite a lot of electricity flowing for a short time. When big fault
currents like this flow, they can 'clear' the fault by burning away the
metal bits wot are touching where they shouldn't be - so explaining your
'well now it doesn't trip the MCB any more!' observation.

HTH - Stefek


it does however raise the worrying question as to what would have happened
to any insulation in the immediate vicinity of this self-righting
extraneous-metal-bit-vapourising fault, though.

--