View Single Post
  #11   Report Post  
AutoTracer
 
Posts: n/a
Default

You could try to localize the break using a signal tracer like "fox and
hound" You would attach the signal source to one end and use the sniffer to
follow the wire until the signal ends. At that point, you should find your
open.

You may also be able to (and I have not verified it yet, its just an idea)
to use one of those stud finder like things that also detects electrical
wiring. you may need to reverse the hot and neutral since they detect the
AC on the hot wire.

If that wire runs horizontally and has no staples you can use it to pull a
new wire but if not, it may be easier to abandon the old wire in place and
run a new conductor along any route that is easily accessible to you. If
you're lucky, you can minimize the damage to a few well placed holes in the
wall.

Definately worth a little more time trying to localize the open releative to
the work required to replace. Maybe you can punch a hole in the wall part
way along the line so you can divide the wire in half for continuity
testing/isolation.

A temporary short can fuse open a conductor ending up in an open if the
breaker is defective. For safety sake, verify the breaker's operation at
some point if the exact cause of the open is not discovered.

Hope to see you post the solutution later



"bill a" wrote in message
m...
Now that you mention that the wiring is aluminum, it becomes much more of
a possibility that
the neutral conductor does have a break. Aluminum wire is way more prone
to fatigue
cracking than copper.
Sometimes the fatigue breakage is caused by thermal cycling and the
associated wire movement.
A break in this case would be likely to occur fairly close to a screw
terminal or wire nut.
You might, therefore try your continuity check by probing the conductor an
inch or two back
from the each end of the wire.
hth
bill



"Peter" wrote in message
...
House wiring is about 25 years old (built 1979). Aluminum wiring.

Residential home. I did check other outlets, lights, breakers etc.
They all
seem to work. Voltages at the breaker panel measured about 130 volts to
a ground wire. (I did not test to neutral). Voltages at all receptacles
is
in the range of 124.6 to 124 8.


So it was easy to narrow down to one circuit.
I pulled apart the switch boxes, and two fixtures, plus a ceiling box
that was
originally used for a ceiling light, checking all connections.

There is power up to a receptacle
box..... and (after testing continuity at different boxes) I finally
got to
the point where I could identify the first ceiling fixture junction box
after
the receptacle. At this fixture junction I removed the fixture and
pulled apart the hot
and neutral connections andcontinuity tested every wire using a DVM to
find which
pair of wires went to the receptacle and which continued to other
fixtures.

And then, I connected the two wires together at the fixture junction
box (power
off)..... and disconnected them from the preceding receptacle.. No
continuity in this
loop. I checked the hot (black) from receptacle to fixture and that had
continuity. but
the neutral did not.

Also powered on the circuit and used a light probe to ground to check for
voltage. There
was voltage
at the first fixture junction box and nothing at anything beyond that
point..
which makes sense because I had disconnected everything else from
that fixture box.

A three prong electrical tester showed all receptacles to be wired
correctly.

I was up in the attic looking for squirrels, there was no way they could
have
gotten to the wiring.

That's why I'm confused because usually wires in the wall are usually
solid,
except when conditions change for whatever reason, construction, damage
overheating, etc. But everything was normal...and suddenly it didn't
work.

I don't have much more than the standard experience with switches,
fixtures
and receptacle so feel a little over my head at this point.









On Thu, 02 Jun 2005 09:43:10 -0400, Phil Munro
wrote:

Perhaps you should tell us whether or not you knob and tube wiring,
and what the age of the house is. It your wiring is K&T, then it is
definitely possible that a junction inside a wall/ceiling area is bad.
Otherwise, everything shared by others should be considered. --Phil

Peter wrote:
Help and expertise desperately needed....

My kitchen lighting circuit is not working.

Circuit breaker checks out and I have a ceiling/fan and receptacle in
another room on the same circuit that works. When checking the romex
cable coming off the receptacle to the first kitchen light..the black
wire
has continuity, but the white (neutral) does not. I disconnected the
wire
pair at both ends, (fixture and receptacle) and connected wires
together.
Tested with no continuity.

Final test.... I ran another neutral from the panel to the first
fixture and all the
lights are working.

So it looks as if the neutral is defective. But it's about 15 feet
away
from the fixture, traveling inside a wall and through the ceiling.

How does one replace a cable run in the wall. Does this mean
tearing down the sheetrock both on the ceiling and in the wall???

Are there tools or meters available that test out a break in a wire ???

I'm thinking that hiring an electrician might be a good idea ??? Can
they
do this job faster than a DIY'er and approximately what would they
charge ??

Thanking you in advance for your help and recommendations !!!

Peter