Robert11:
It's the current (not the voltage) that you should be most worried about....
your meter is probably sensitive enough that you are seeing voltage from
leakage or capacitive coupling Put a 1.0 K restore in parallel with your
meter probes.... if you still measure much more than 0.2 V RMS then you
might have a problem.
--
Best Regards,
Daniel Sofie
Electronics Supply & Repair
- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -


"Robert11" wrote in message
...
Hello:

Have been trying to get some smoke detectors interconnected, and
during the trouble shooting of the problem, I measured (with an analog
voltmeter) the
voltage between the white neutral, and the bare copper ground wire in the
box.

Was very surprised to see that it was about 2 V AC.

Other than the fairly obvious reasons, such as bad ground connections in

the
service box for the neutral or gnd, or within the wiring chain itself,

was
wondering if anyone might have any other thoughts or opinions on this.

Might as well add this: The smoke detectors were on line, and functioning,
when I measured.
The interconnect for the smoke detectors (the third, red, wire ) uses the
white neutral (also)
as it's return. And, measuring a few outlets around the house showed 0
voltage between the neutral and gnd as one would expect.

But, even if the smokes were dumping something on the white neutral, it
being at gnd potential, would "sink" these voltages immediately, I would
think, if the neutral was grounded well.
So, what might be happening ?

BTW: How "common" is it to see voltages of this magnitude between the

white
neutral and ground ?

Thanks,
B.