View Single Post
  #3   Report Post  
John Rumm
 
Posts: n/a
Default

wrote:

Remote brick built shed, originally wired up by a previous owner. Fed via


How remote?

Proposed new set up:
3core 4mm SWA - earth is taken through the yellow wire - with the armour
sleeving bonded to the yellow wire at both ends.


What type of earthing do you have at the house?

You may not want to export the house earth if it is either a TT setup,
or if the shed is a long way from the house. If this were the case then
you could connect the earth to the shield at the source end, but
terminate in a plastic CU at the shed end and provide a local earth via
a rod.

Two way CU in the shed with mcbs and protected by integral 30mA RCD.
Sockets (probably three) in the shed, either as a ring main or as a radial
circuit, plus an external socket mounted externally on the shed wall for
garden use.
- 2.5mm T&E fed from a 16A mcb

Shed lighting plus external light
- 1.25mm T&E fed from a 6A mcb


1mm sq will be more than adequate for the lights on a 6A MCB.

What sort of work are you planning to do in the shed - how critical is
the loss of light on a RCD trip going to be?

If it is an issue you could fit a battery backed emergency light (about
30 quid from TLC).

In-house connection is to a 32A mcb on a split CU and is protected by the
integral 30mA RCD in the CU (there are two split CUs in the house, this CU
only feeds shower and outside lights, so if it trips it's not a problem).


Since it is protecting the shower, changing it for a higher trip rating
or a time delay version is not really an option. So that kind of negates
any benefit of the one in the shed.

SWA terminated in the shed and indoors in a metal knockout box using
suitable glands. Metal box is also earthed (I assume that a plastic box
could be used instead if required?)


If you are not going to export the house earth then plastic somewhere
(i.e. either the box or the CU) will be needed to isolate the shield.
You can usually take a SWA straight into a CU - it should have a 20mm
knock out that will take a gland)

I realise that this means that the shed light will be lost if the RCD
trips in the shed. I could solve this by using a separate CU in the shed
for lighting only (I have a spare CU) or is this not permissible as the
light would still be lost if the 32A mcb tripped in the house CU?


It is not the house MCB that is likely to trip, but the house RCD. A
imbalance fault at the shed could trip either the shed, the house or
both RCDs

An alternative would be to use the existing supply from the fused spur on
the ring main to feed a separate CU in the shed just for the lighting,
using a 5A fuse in the spur instead of the current 13A one. However, I
would have liked to have got rid of that cable altogether.


Battery backed light in the shed sounds like a whole lot less fuss.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/