View Single Post
  #17   Report Post  
andrewpreece
 
Posts: n/a
Default


"Andrew Gabriel" wrote in message
...
In article ,
"andrewpreece" writes:

"Andrew Gabriel" wrote in message
...
In article ,
"andrewpreece" writes:
Hello Folks,
Looking at my earthing (TN-S) I see a 6mm2 earth wire come from

the
service head thingy

That sounds more like TN-C-S.
For TN-S, the earth conductor would come from the cable sheath
under the service head.


Thanks Andy. I understood that TN-S is most common for urban houses, and
that there would
most probably be a sign saying so if it was PME (TN-C-S ). I can't
immediately see why if the sheathed cable enters the service head/cutout
that means it's TN-C-S. Is there a foolproof way to tell?


Look at the FAQ:

http://www.diyfaq.org.uk/electrical/...al.html#system

Alas, having looked inside the service head, I can identify the live
conductor, red
insulated and central to the cable. Surrounding the red core are then some
16(?)
smaller black insulated wires that are stuffed into a terminal to make
neutral.
There are then four bare copper conductors of the same size that go to the
earth block.
Thinking about it, I have no idea whether these are dedicated earths or
simply
four neutral wires with their black insulation stripped back out of sight in
the cable,
and co-opted into being earths, in which case I have TN-C-S. Why is nothing
ever
easy?

Service bonding should normally be 10mm2.
Main earth conductor to supplier's earth connection should be 16mm2.


I've read conflicting stuff about this - some say the size of service
bonding depends on the earthing type in question.


It does. I gave you the figures which cover most residential
installations. In theory, your supplier can ask for larger
conductors in some cases too.


I think you're right about the 16mm2 - I 've just found a website that gives
16mm2 as the size of the main earth conductor for TN-S. And TN-C-S.

16mm2 is out of the
question - the CU won't take 16mm2 nor will the brass earth terminal on

the
service head: you're going to say now I should get the 'lectric company

in
to replace my service head........ :-(


I don't think I've seen such a service head, except possibly a 5A
one in the base of a streetlamp column. Does this or the CU have
multiple terminals -- if so you can split the conductor strands
into two terminals. Otherwise, I guess you're stuck with using
10mm2, which is probably OK if you only have a 60A cutout.


I was wrong, the service head will take 16mm2, it was difficult to see, all
covered in dust
at at a bad angle.

(2) I have some BS951 clamps which are a puzzle to me: I thought that

one
threaded the strap through the clamp and tightened the screw, which

would
tighten up the clamp on the pipe, but what I
took to be the clamp section ( it has the earth terminal attached to

it )
does not move at all when the screw is tightened ( yes I backed the

locknut

The strap goes round the pipe and then through the slots which raise
it off the pipework a second time.
Pull the strap tight with pliers and bend it sharply where the
tail exits the bracket to stop it slipping back in. Then the screw
clamps onto the strap, deforming in the bracket and pulling it
tight on the pipe. The screw should not touch the pipe itself, nor
deform the strap enough that it is pushed back onto the pipe under
the bracket -- if it does, you didn't pull it tight enough to start
with or it slipped back through the bracket before you got it tight.
Once you've used a clamp, the strap is deformed and cannot be reused.


I figured pulling the strap tight with pliers might work. However, the

screw
does not deform the strap
pulling it tight. The strap sits in the U portion of a metal stamping

shaped
thus:- U¬ , which is held in position by the rest of the clamp. All

that

Sorry, but I can't picture what you're doing wrong.
Can't find any web pictures to point you at either.


See my earlier post - think they need disassembly then reassembling
slightly
differently. I think they may be assembled that way to keep them all in one
piece
during transportation.

(3) I believe that it is unnecessary to run an earth cable to my

bathroom
( which has no bonding at all ), and that merely bonding all the

exposed
metal bits to each other with 4mm or protected 2.5mm cable is

OK??????

Yes. It should be connected to an earthing terminal in the bathroom
(ideally the earths of all circuits in the bathroom), but does not
need a dedicated run back to your main earthing terminal.


What passes for an earthing terminal in a bathroom? I have no electrics

in
my bathroom.


In that case, just bond.


OK -thanks.

--
Andrew Gabriel