"Ned Simmons" wrote in message
...
In article ,
says...

"Ned Simmons" wrote in message
...

But those 20A receps must be protected by 20A overcurrent
protection and the CBs in your panel aren't qualified for
branch circuit overcurrent protection.


Huh???


I thought that was pretty clear. Do you have a specific
question or comment? "Huh???" is pretty vague.


Well, it begs an explanation for a statement that is completely against NEC
and the purpose of Circuit Breakers. Of course the breakers in your panel
are qualified for branch circuit protection. That is in fact, exactly what
they are there for. Obviously, you mean to state something else but the
vague nature of the way you have either made statements like the above and
the included NEC text without explanation of the point you are trying to
make, causes it to be difficult for others to understand what you are
saying. I can't argue with a lot of what you're trying to say, because I
can't understand what you're trying to say. There's one thought that is
occurring to me and that is that you are using the word "panel" to refer to
the unit being sold by the OP that started this whole thread as opposed to
the breaker panel in the house. Throughout this thread we have used the
word panel to refer to the later. If my guess is true then I do understand
what you are trying to say and in fact I agree. But, that's a guess and if
my guess is wrong then there's something very wrong in what you are saying.




NEC's definition of "Branch Circuit":
"Branch Circuit. The circuit conductors between the final
overcurrent device protecting the circuit and the outlet
(s)."


I don't understand what the purpose of this quote is. It does not

relate to
what you typed immediately above it.


It relates to my use in the previous paragraph of the term
"branch circuit", which has a very specific meaning in the
NEC.


It would have been a lot more beneficial to explain yourself briefly instead
of a reply like this which is really quite obtuse. Clearly at least one
person here is not getting the point your are trying to get across and this
response does nothing to clear that up.




For starters:

"240-3. Protection of Conductors
Conductors, other than flexible cords and fixture wires,
shall be protected against overcurrent in accordance with
their ampacities as specified in Section 310-15, unless
otherwise permitted or required in (a) through (g)."

See 210-24 for requirements for protection of receps.


Again - why post this quoted text? The branch circuit is protected in

the
panel.


Not if you were to take the suggestion made in the first
post in this thread, and repeated in other posts, to feed
the panel from a larger than 20A circuit.


Ok... but again, simply quoting NEC without an explanation of why you are
quoting it - an explanation of your objection which uses the NEC as
validation, does nothing to further a conversation, or (if it is your
intent) the understanding of the poster in error.
--

-Mike-