View Single Post
  #34   Report Post  
Gymmie Bob
 
Posts: n/a
Default

All semantics!

It doesn't cost anymore for me to heat my home to 69 deg or 72 no matter
what the humidity in the summer.

Forgot a big factor boys.

"Abby Normal" wrote in message
oups.com...
Turning down from 69.7 to 69 is not going to do much, lets get frugal
and look at keeping a home at 69 instead of 72.

Compare 72 @ 29% to 69 @ 36%, similar enthalpy. Almost think Lennox had
a typo. Look forward to seeing their new brochure, to see if in fact
you have basically pointed out a typo. 72 @ 29% vs 69 @ 35%, or 72 @
19% vs 69 @ 25%

2400 sq ft with a conductance of 400 btu/(hr F), again this is heat
conducting out of the house.

Air infiltration equivalent to 160 CFM.

So setting thermostat down from 72 to 69 saves 3 x (400 +1.08 x 160) =
1718.4 Btu/hr.

As a check, assuming 70F indoor temp, 0F outdoor temp, heatloss of home
in the ball park of 70x (400 + 1.08 x 160)= 40,096 Btu/hr. Wow a 45 MBH
90% eff gas furnace would be right on the money, and this is typically
the smallest size condensing furnace on the market, so this scenario
sounds realistic.

The house volume is about 19,200 cubic feet so the difference in the
amount of water held in the air is a little under one pound and the
heat to evaporate this moisture will be a maybe 900 Btu.

Save 1718 Btu then waste 900 to evaporate some water.

So there is a 'savings' of 818 Btu.

Yes the motors that turn humidifier drums use energy, but energy is
conserved and ultimately this energy creates heat in the home as well,
so it is not wasted.


wrote:
OK Nick, care to elaborate on what your theory is?


Sure. Here's the email I sent to Lennox...

Sent: Monday, January 17, 2005 8:58 AM

Subject: Attn: president/legal--Winter humidification wastes energy

Gentlemen,

I suspect that winter humidification wastes vs saves heating energy,

and
the savings claim is an energy myth. People tend to forget that

evaporating
water takes heat energy, and that heat energy has to come from

somewhere,
even if something like a humidifier belt motor uses little energy by

itself.

The heat saved by turning a thermostat down appears to be far less

than
the extra heat used to evaporate water, in all but extremely tight

houses
with little insulation, eg submarines.

http://lennox.com/pdfs/brochures/Len...umidifiers.pdf
claims
that 69 F at 35% RH and 72 F at 19% RH are equally comfortable, but

the BASIC
program in the new ASHRAE 55-2004 comfort standard predicts that 69 F

and 35%
RH and 69.7 at 19% RH are equally comfortable (PMV = -0.537, see

below.)

If a 2400 ft^2 tight house has 0.5 ACH and say, 400 Btu/h-F of

conductance,
turning the thermostat down from 69.7 to 69 saves (69.7-69)400 = 280

Btu/h.

Air at 69 F and 100% RH has humidity ratio w = 0.015832 pounds of

water per
pound of dry air, so 19% air has wl = 0.00301, and 39% air has wh =

0.00617.
Raising 69 F air from 19 to 39% requires evaporating wh-wl = 0.00316

pounds
of water per pound of dry air. Dry air weighs about 0.075 lb per

cubic foot.

With 0.5x2400x8/60 = 160 cfm or 9600 ft^3/h or 720 pounds per hour of
air leakage, raising the indoor RH from 19 to 39% requires

evaporating
720x0.00316 = 2.275 pounds of water per hour, which requires about

2275
Btu/h of heat energy, so it looks like humidifying this fairly

airtight
house wastes 2275/280 = 8 times more energy than it "saves." And many


S houses are less airtight, so humidification would waste more

energy.

Please modify your energy-savings claim.

Thank you.

Nick Pine

10 SCREEN 9:KEY OFF
20 CLO=1'clothing insulation (clo)
30 MET=1.1'metabolic rate (met)
40 WME=0'external work (met)
50 DATA 69,35,69.74,19
60 FOR CASE=1 TO 2
70 READ TC,RC
80 TA=(TC-32)/1.8'air temp (C)
90 TR=TA'mean radiant temp (C)
100 VEL=.1'air velocity
110 RH=RC'relative humidity (%)
120 PA=0'water vapor pressure
130 DEF FNPS(T)=EXP(16.6536-4030.183/(TA+235))'sat vapor pressure,

kPa
140 IF PA=0 THEN PA=RH*10*FNPS(TA)'water vapor pressure, Pa
150 ICL=.155*CLO'clothing resistance (m^2K/W)
160 M=MET*58.15'metabolic rate (W/m^2)
170 W=WME*58.15'external work in (W/m^2)
180 MW=M-W'internal heat production
190 IF ICL.078 THEN FCL=1+1.29*ICL ELSE FCL=1.05+.645*ICL'clothing

factor
200 HCF=12.1*SQR(VEL)'forced convection conductance
210 TAA=TA+273'air temp (K)
220 TRA=TR+273'mean radiant temp (K)
230 TCLA=TAA+(35.5-TA)/(3.5*(6.45*ICL+.1))'est clothing temp
240 P1=ICL*FCL:P2=P1*3.96:P3=P1*100:P4=P1*TAA'intermed iate values
250 P5=308.7-.028*MW+P2*(TRA/100)^4
260 XN=TCLA/100
270 XF=XN
280 EPS=.00015'stop iteration when met
290 XF=(XF+XN)/2'natural convection conductance
300 HCN=2.38*ABS(100*XF-TAA)^.25
310 IF HCFHCN THEN HC=HCF ELSE HC=HCN
320 XN=(P5+P4*HC-P2*XF^4)/(100+P3*HC)
330 IF ABS(XN-XF)EPS GOTO 290
340 TCL=100*XN-273'clothing surface temp (C)
350 HL1=.00305*(5733-6.99*MW-PA)'heat loss diff through skin
360 IF MW58.15 THEN HL2=.42*(MW-58.15) ELSE HL2=0'heat loss by

sweating
370 HL3=.000017*M*(5867-PA)'latent respiration heat loss
380 HL4=.0014*M*(34-TA)'dry respiration heat loss
390 HL5=3.96*FCL*(XN^4-(TRA/100)^4)'heat loss by radiation
400 HL6=FCL*HC*(TCL-TA)'heat loss by convection
410 TS=.303*EXP(-.036*M)+.028'thermal sensation transfer coefficient
420 PMV=TS*(MW-HL1-HL2-HL3-HL4-HL5-HL6)'predicted mean vote
430 PPD=100-95*EXP(-.03353*PMV^4-.2179*PMV^2)'predicted %

dissatisfied
440 PRINT TC,RC,PMV
450 NEXT CASE

69 35 -.5376486
69.74 19 -.5372599

Engineering VP Mark Hogan said Lennox was embarrassed by all this and
he didn't know where their numbers had come from, and he thanked me
for bringing this to their attention and said they are changing their
printed brochures and Aprilaire web site energy-savings claim.

This reminds me of David and Goliath :-)

Nick