Ignoramus21628 wrote:
On Mon, 17 Jan 2005 20:37:24 GMT, HorneTD wrote:

Those outdoor panels are available with feed through lugs off of the
main buss bars that will feed the entire ampacity of the panel's main
breaker to the panel they supply. Since that panel will be located
outdoors the inlet for the generator cord can be close nippled to the
panel's enclosure.



Tom, can you please explain in a little more detail what configuration
do you mean here. Thanks!

i


The link below is to a document that goes over the installation of the
interlock kits in outdoor square D load centers.
http://ecatalog.squared.com/pubs/Electrical%20Distribution/Load%20Centers/Accessories,%20QO%20(LK,%20PK,%20QO,%20QON)/40273-809-02.pdf

One of the load centers available is equipped with feed through lugs on
the end of the buss bars that allow you to run the entire ampacity of
the panels main breaker to another panel. When this panel is equipped
with a the interlock kit shown in the previous link the panel will serve
as a transfer switch. The panel can be viewed at
http://ecatalog.squared.com/fulldeta...B#digestinf o

I hope that answers the question.
--
Tom H