Lurch wrote:
On 18 Dec 2004 09:32:58 -0800, strung together
this:

Can you explain why its bad to have a spur from a spur? everything

is
working fine even if I put the dishwasher on at the sametime. There

is
always power going to the tub.

The idea is that if you start adding spurs to spurs etc... and

loading
each spur to the max then the length of cable from the first is at
risk of overheating\loading.
It's a blanket rule that has always been adhered to, even though one
spur with 13A on it equates to 13 spurs with 1A each on them it's not
the done thing. In the future someone could come along without

knowing
this and start loading up all the spurs and overload the first leg of
the spurs.
--

SJW
Please reply to group or use 'usenet' in email subject


Gotcha, thanks for your help. I checked the hot tub its currently
plugged into a weather proof outside single socket with RCD protection
and its rated at 13AMP so the FCU option should be fine.
cheers again

Richard