Thread: Gas Pipe
View Single Post
  #6   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Mon, 18 Oct 2004 19:26:38 +0000, alan wrote:

Just because it is substandard does not mean you have to repipe it, you are
only "obliged" to do that if you are a professional, it would seem the
proposal would improve the piping capacity.
I had a telephone conversation with CORGI last year and who are aware the
advice they give out, if followed slavishly, would create havoc ie "gas
pipework undersized so that a gas appliance cannnot run at the
manufacturer's design input pressure (and flow)" = AT RISK
Well that would knock out around 80-90% of gas appliances.
The tech guy gave his opinion that cookers would be ok to 14mb, probably
the same for boilers, especially modern modulating, but he would not firmly
give this figure for boilers as there are too many variances.
The only real danger is cookers and some gas fires on a low peep can be
extinguished by the boiler kicking in, but this only happens well below
14mb.


Yes and No. the 80-90% is probably a fair estimate. However most are only
a little out of spec. As 90%+ of installations that don't comply would
comply if the maximum permitted pressure drop were 3 mb insteadd of 1mb.

I agree that few appliances would have a real problem at 14mb
(except some forced premix burners which are quite sensitive).

AIUI there is an absolute minimum for Transco to supply gas at 15mb with a
1mb drop in the installation pipework that makes 14mb.

The problems of course occur when then you have both very poor service
presure and poor installation pipe work.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html