Another subpanel grounding question
xrongor wrote:
in addition to what has been said, i believe code states that if your
garage/shop is in a seperate building, not only do you need to ground it
back to the panel in the house via a wire, but you need two grounding rods
sunk in the ground at the garage.
so in short, i think you need both if you want it to be 'correct'
randy
"Korey Atterberry" wrote in message
m...
Hey all-
First off, I apologize for asking a question that seems to be asked
a lot around here. I've been reading posts on the subject for about 2
hrs this morning, but I'm missing something.
My situation: I have a main panel in my house, and I have an
attached garage which my dad and I put a 60amp subpanel in. Now I
know that I need to keep the neutral and ground separate in this
subpanel (I've seen LOTS on this topic), but what I'm missing is,
where do I connect the grounding bar in the subpanel? Grounding rod,
ground wire back to the main panel, don't need it?
Right now we've got (and I know our setup is wrong) the main lug
subpanel with just one bus bar, which is not connected to the case.
Both the ground and neutral wires for the branch circuits for this
panel are connected to this bar. We have two hot wires and one
neutral run back to the main panel where I have a 60amp breaker. The
inspector has been out and given the system his blessing (which makes
me doubt him a bit). My dad did most of the work, I had second
thoughts after the inspection, so that's why I'm here.
So to correct the situation, I presume I need to get a grounding bar
kit for the subpanel and hook the branch circuit grounds to it
(keeping the neutral isolated from the ground). But what do I hook
the grounding bar to? Do I need a grounding rod or a ground wire back
to the main panel?
Thank you in advance,
Korey
Actually, if the subpanel is in a separate building, you have the option
of *not* running 4 wires back to the main panel. There are restrictions
on this 3-wire method, of course. All this is moot because OP said it
was an attached garage.
Bob
|