  #9   Report Post  
Posted to alt.home.repair
bruce bowser bruce bowser is offline
external usenet poster
 
Posts: 180
Default Wire size?

On Monday, January 4, 2021 at 4:56:33 PM UTC-5, wrote:
On Mon, 4 Jan 2021 07:58:40 -0800 (PST), trader_4
wrote:
On Monday, January 4, 2021 at 10:10:43 AM UTC-5, Ralph Mowery wrote:
In article 1656f0a31b067245$2$168419$4206dc53
@news.newsgroupdirect.com,
says...

I put an automatic gate in but I did not know that I was going to when I built the house. I have a GFI outlet on the back of my house about 200 feet from where I need power. What size wire should I use. Its 110v

--


Others mentioned you need to list the current of the load.

One other thing is that 200 feet may be too long.

Numbers vary from 150 to 250 feet is the maximum length of wire from the
outlet to the load of a ground fault outlet. They may trip from the
internal leakage of the wires if long enough.

I use the term internal leakage very loosley as there can be several
factors determining the tripping due to wire length.


Good point. IDK what the code says regarding electric gates and GFCI. But he
may be better off running it non-GFCI to the gate and then installing a GFCI there,
just before the gate. Having a GFCI receptacle at the gate might be a good idea
too, handy for future repairs, plugging in a chain saw, Xmas lights, etc.


One issue might be burial depth. A 120v 15 or 20 amp GFCI protected
circuit on residential property only needs to be 12" down.

Otherwise
it is 18" for pipe and 24" for direct burial cable.


Or just 2" if the conduit is through rock (with not less than 2" of concrete) and 24" if the conduit goes under a street or road off of the property (as per code NEC table 300.5, figure 300-7).

The max length on a GFCI circuit is also manufacturers erring on the
safe side. I don't even have a clue how much wire is on the circuit in
my screen cage and out to the shed but it is way over 250 feet total.