On 22/11/2019 10:20, Andy Burns wrote:
Tricky Dicky wrote:

the readings I got was 1.8 Ohms for the CPC and 0.8 Ohms for both Live
and Neutral. Are these OK?


Assuming 2.5 T&E with 1.5 CPE, you'd expect 0.8*1.67 = 1.3 ohms for the CPC

Worth checking for some terminals in need of tightening? An outside
chance of a section of older T&E with 1mm CPC?


I would go for a loose connection unless most of the cable has a 1mm
CPC. Based on 0.8 x 2.5 = 2.

--