Earth Bonding
On 22/11/2019 10:20, Andy Burns wrote:
Tricky Dicky wrote:
the readings I got was 1.8 Ohms for the CPC and 0.8 Ohms for both Live
and Neutral. Are these OK?
Assuming 2.5 T&E with 1.5 CPE, you'd expect 0.8*1.67 = 1.3 ohms for the CPC
Worth checking for some terminals in need of tightening? An outside
chance of a section of older T&E with 1mm CPC?
I would go for a loose connection unless most of the cable has a 1mm
CPC. Based on 0.8 x 2.5 = 2.
--
Adam
|