View Single Post
  #7   Report Post  
Posted to uk.d-i-y
[email protected] nothanks@aolbin.com is offline
external usenet poster
 
Posts: 1,037
Default To export an earth or to TT from an RCBO?

On 02/09/2019 18:02, ARW wrote:
On 02/09/2019 08:51, wrote:
On 01/09/2019 14:54, ARW wrote:
On 31/08/2019 09:57,
wrote:
On 30/08/2019 19:49, ARW wrote:
On 30/08/2019 19:08,
wrote:
I have a couple of external sockets that are fed from an RCBO
which also provides power (via about 30m of buried 3-core SWA
cable) to a class II Well pump and controller. The SWA armour and
earth conductor are connected to the house earth solely by the CPC
in the T&E cable. I'm wondering about putting a small
weather-proof CU at the Well so I can use its supply for a remote
socket, garden lights, and maybe a gate controller. The question
is whether to TT the remote CU (but the SWA will still have to be
fed from the RCBO) or whether to add a 10mm earth cable between
the MET and the SWA armour so I can use the exported earth. The
house has a dedicated TN-C-S supply from a 2-wire overhead feed,
but I have fitted an additional ground rod so (hopefully) the loss
of the supply neutral should not cause a safety issue.

What would the experts do?

You cannot make a TT supply from a 30mA RCBO.


I can see a possible issue with discrimination, but if the RCBO (or
RCD) is just measuring L-N current imbalance then why would there be
a functional problem?

Other than discrimination it would work.

So, the question becomes: which is the lesser of the two evils, to
export an earth or to have an RCBO and RCD in series? I'm leaning
towards the latter because it's in the nuisance category, whereas
exporting the earth leads to a possible (but unlikely in this case)
safety issue.
Hmmm, further thought ... if I were to export the earth I would need
to lift a lot of floorboards to run an earth wire back to the MET from
the SWA termination, but these are the same boards I would have to
lift to run a dedicated T&E cable back to a spare MCB in the CU. My
conscience is now telling me that I should run the T&E and do a
"proper" TT job from a dedicated MCB.

This DIY group has been useful yet again. In asking and discussing a
question it forced me to think about the problem in a different way.


Why is the SWA RCD protected?

In "plan A" it was because there's an external socket (fed from an RCBO)
on the end of the house nearest to the Well - a convenient point to take
the SWA from. However, I've decided to "do it right" and lift the
floorboards to put in a dedicated T&E feed to the SWA from an MCB.

And you do not have to export the earth as a main equipotential bond
unless there are extraneous conducive parts.

Currently the pump and controller are class II, but if I have a small CU
at the tail of the SWA then I can't predict what might be connected in
the future. But that all goes away if it's TT'd.