Default How common is TN-C-S household wiring in the UK with combined PEN

Martin Brown wrote:

On 18/06/2019 21:42, ARW wrote:
On 18/06/2019 10:01, Andy Burns wrote:
Robin wrote:

Martin Brown wrote:

So how common is TN-C-S with a single PEN in new build?

I'm sure Adam can add more datapoints than everyone else here combined.


I am also sure that I am not sure. New builds in Epworth that I have
just worked on (one street). Half are TN-C-S with a 100A supply and half
are TN-S with a 80A supply.


Thanks. You would think it made more sense to do one or the other.

However I would say that 80% of newbuilds I have worked on in the last
20 years are supplied with a single core concentric cable.


So the incoming armoured cable has a live core and outer PEN sheath?

I expect it is against the wiring code but is there anything to prevent
the householder having a stake in the ground bonded to the household
protective earth in addition? It won't make a blind bit of difference
most of the time but if the neutral return ever fails then at least you
don't suddenly find every household appliance is live to the touch.


A simple earth stake can't do any harm, but it is not necessarily going
to make that much difference to the potential reached during a neutral
fault. Say the active loads on the supply beyond the fault add up to
about 5kW, resistance 12 ohms. And the best likely stake gives 100 ohms
earth resistance. Then it is only going to reduce the final voltage on
the house earth by about ten percent.

--

Roger Hayter