View Single Post
  #6   Report Post  
Posted to uk.d-i-y
GB GB is offline
external usenet poster
 
Posts: 4,768
Default How Can This Happen (Electrical)?

On 28/02/2019 14:38, dennis@home wrote:
On 28/02/2019 14:15, Paul Herber wrote:
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Earthed via a the ring-main circuit?




Probably not, RCDs don't just detect earth leakage but any current
imbalance between live and neutral.

It wouldn't actually matter where it was earthed if there was leakage to
earth and it wouldn't affect other circuit unless they also had an earth
leakage problem as RCDs aren't connect to earth.



Quite agree. I think Clive is probably right as to the cause. Within the
consumer unit, all the lives and all the neutrals are connected
together, so there's scope for some coupling between circuits. The only
thing that's really surprising (to me) is that the RCD protecting the
lighting circuit does not trip.

(I may be making a fool of myself here. Hope not!)