On 30-Dec-2003, "Charles" wrote:


I have followed suit and grounded a few outlets
upstairs by running separate ground wire to this same pipe. This is
probably not strictly code, but I think it's safe.



I don't know about the US, but it's illegal in Canada. I doubt it's
allowed in the US too.

Mike


Actually the US NEC does permit the connection of an Equipment Grounding
Conductor (EGC) to a grounding electrode such as the first five feet
within the structure of an underground water pipe that has ten or more
feet in contact with the earth. The applicable section is quoted below.
--
Tom Horne

VII. Methods of Equipment Grounding
250.130 Equipment Grounding Conductor Connections.
Equipment grounding conductor connections at the source of separately
derived systems shall be made in accordance with 250.30(A)(1). Equipment
grounding conductor connections at service equipment shall be made as
indicated in 250.130(A) or (B). For replacement of non-grounding-type
receptacles with grounding-type receptacles and for branch-circuit
extensions only in existing installations that do not have an equipment
grounding conductor in the branch circuit, connections shall be
permitted as indicated in 250.130(C).
(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions.
The equipment grounding conductor of a grounding-type receptacle or a
branch-circuit extension shall be permitted to be connected to any of
the following:
(1) Any accessible point on the grounding electrode system as described
in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the
branch circuit for the receptacle or branch circuit originates
(4) For grounded systems, the grounded service conductor within the
service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar within the
service equipment enclosure