View Single Post
  #112   Report Post  
Posted to uk.d-i-y
John Rumm John Rumm is offline
external usenet poster
 
Posts: 25,191
Default So how much power does an oil filled radiator actually use.

On 15/11/2017 17:28, Andy Burns wrote:
whisky-dave wrote:

John Rumm wrote:

If the voltage sags too far, then you get lower PSCC so can expect
slower operation of protective devices under fault conditions, so
increase electrocution risk, and catastrophic cable failure risk.


But not in under 3 hours.


The 3 hours at 40+ Amps is the "slow" part of the MCB curve, in the
event of a short circuit you want sufficient current to ensure it trips
within the "fast" part of the curve ...


Indeed...

You need 160A to make sure a B type MCB will trip in the magnetic part
of its response curve and that implies a maximum loop impedance at the
point of the fault of 230 / 160 = 1.44 ohms [1]

Even if the circuit is in spec and meets that requirement at all
sockets, running at only 202 volt gives a reduced potential worst case
PSSC of 202 / 1.44 = 140A, which could leave you on the thermal portion
of the response curve and *20 seconds* away from disconnection. (and
that ignores the effect of elevated conductor temperature on the loop
impedance)



[1] I am assuming that the wiring was done before 17th edition amendment
3 and the 5% reduction in Cmin.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/