On 29/05/2015 18:59, dennis@home wrote:
On 29/05/2015 01:40, John Rumm wrote:
On 28/05/2015 18:56, ARW wrote:
Of course some people still bang on about balancing the loads on a ring
circuit and mention portable electric heaters to back up their
statements.
They also ignore the point that a 20A protected radial could run
indefinitely with a pair of 13A fan heaters, and a cable de-rated to 20A
- but that would also spoil their argument. ;-)
Which cable is rated at 20A?
Not 2.5 mm T&E.
Yes the 2.5mm T&E may be rated at only 20A (and that would be the lowest
acceptable de-rated value permitted in a 20A radial or a 32A protected
ring).
See for example 2.5mm^2 T&E, reference method A:
http://wiki.diyfaq.org.uk/index.php?...es#Cable_Sizes
You can also calculate any required de-rating based on circumstances.
It is explained it in great detail he
http://wiki.diyfaq.org.uk/index.php?...g_A_Cable_Size
--