Default #6 NM wire in 1/2" hole?

On Saturday, August 2, 2014 3:58:37 PM UTC-4, wrote:
On Sat, 02 Aug 2014 10:36:24 -0400, wrote:



On Sat, 2 Aug 2014 05:51:37 -0700 (PDT), trader_4


wrote:




On Saturday, August 2, 2014 12:40:28 AM UTC-4, wrote:


On Fri, 01 Aug 2014 23:34:13 -0400,
wrote:







On Fri, 01 Aug 2014 00:32:34 -0400,
wrote:







On Thu, 31 Jul 2014 20:25:57 -0700 (PDT),
wrote:







SMZ42H46ZOGX








When I look this up I do see where the manual says you need 6 ga wire




but it also says "Minimum circuit ampacity 26a" which would be 10




gauge copper according to the NEC. It really sounds like the chinese




book writer does not understand the electrical code.








Does the label on the outside unit say "26a" on the minimum circuit




ampacity line?




Maximum over current protection probably says "50a"




26 amps is more than 80% of 30 amps. Generally a circuit should not




excede 80% of the circuit protection rating (fuse or breaker - and I




assume wiring).








That is not what the label says or what it means.




If you look at the U/L marking guide, you will see the 80% is built




into that "minimum circuit ampacity"




+1




This is a specific piece of eqpt on a dedicated circuit. It's not


a circuit for receptacles. The rules are different. Just like a


previous poster thinks you can't have a 50A breaker on 8g wiring for


an AC, when you can, because the rules are different.






Yup, you set a guy's hair on fire if his knowledge stops at the Time


Life "electric for dummies" book. There are places where you can have


12 gauge wire on a 50 and 14 on a 40. It is a common question on the


inspector tests.


(typical was, 1HP 120v, 16 FLA motor on a 40a breaker with 14ga


copper)








I bet the design FLA is more like 19-20a and the actual max you would




ever read with an amp probe is more like 15-16 in normal operation




They say strange numbers like "26a" to keep you out of 12ga which is




rated for 25a in the 60 and 75c column.




The marking guide and the label itself is clearly saying 10 ga copper.








Also, if I remember and read correctly, the




specification is for a "stranded" wire - which "generally" should be




sized up 1 size.








Cite that.




Table 310-16 does not make that distinction




Yes, I'd like to see that too. AFAIK, solid and stranded of


the same gauge have the same current carrying capacity, unless


this AC is connected to a 1Mhz power source, or similar where


skin effect comes into play.




Yup, the stranded is actually better if you start getting up in the


higher frequencies. You can see the effect at 400hz which used to be


pretty common in computer rooms. (back when they actually had real


computers in there) ;-)


The big 400hz cables were usually fine stranded.




If you look at table 8 you will see that the DC resistance of stranded


#10 is actually 0.03 ohms more than solid per 1000 feet but that is


insignificant for this calculation and the difference is a little less


at 60hz




Skin effect doesn't even begin to have any effect in residential or

normal commercial wiring. I know code does not require upsizing for

stranded wire - I never said it did. I said, generally one should use

one size heavier flexible cord than one would use for solid permanent

wiring. I stand by that. Flexible cable is submitted to a lot of

flexing which will eventually compromize some strands, increasing the

resistance.


You have your outside AC units swinging around in the breeze up
there in Canada? Around here, they *are* installed with permanent
wiring, not cords. And the cord reference is in the same lame
drawing, that was obviously written by a buffoon. They confuse
conductors with grounds and call for a 4 conductor cable. As I
already said, even if you allow that they really mean 3 conductors,
plus ground, it's still wrong. The drawing only shows two hots, ie
a normal 240V AC connection. So, following that, we should get a
big old honking 6 gauge 4 conductor stranded "cord". Then leave two
conductors unused. Then let;s call the inspector over and see how he
likes it.

Or we could use two #8 THWN stranded run inside liquidtight. Actually
per the eqpt label, you could use #10, but since the 26A is close to
the max for #10, I'd bump it up.




It is a good idea to use one size heavier cable than

"required", particularly when running close to the design current

limit for the cord.


Cable? Cord? Which is it now? Better rip out all your 14 gauge that's
on 15 amp breakers, make it 12 gauge.




In general practice, MOST people use a cord that is AT LEAST one size

too SMALL for the load.


In general practice around here, people don't install permanent,
outdoor AC eqpt with cords. And I've never seen a 3.7 ton AC unit