In article ,
skeezics wrote:
im wiring my shop and have 2 pieces of equipment i am not sure of. a
true 3 hp compressor and a 3 hp unisaw. is a 20 amp circuit enough for
each or these or do i need to go to 25 or 30 amp? the compressor says
it needs 15.4 amps and the tablesaw says 15.5 amps. thanks all ...


NEC limit for permanently attached devices is 80% of breaker rating.
Which is 16A for a 20A breaker. So, you're OK on _that_ basis.

Then, there is the issue of 'start up' load, vs 'running' load.
Virtually any motor draws more power spinning up, than it does
running 'at speed'. However, with the table-saw, the start-up
current draw is _probably_ not going to approach the draw of a
maximum-load cut. The compressor probably has 'smarts' so that
the motor starts up 'unloaded', and then picks up the load.

Me, I'd 'over-engineer' the solution, and see what happens. After all,
wire is _cheap_. Pull 10 ga. wire, and use a 20A breaker, initially.
Preferably a 'motor rated' (or slo-blow) one, if I can lay hands on it.
In the context of _that_ wiring approach, If the 20A breaker trips too
frequently, it _is_ safe to replace the 20A breaker with a 25A or 30A one.