Roger Mills wrote:
On 10/12/2013 00:37, Bill Wright wrote:
To quote you, "Note that if running the boiler from the genny you will
probably need to make sure that earthing is correctly connected for the
flame sensing to work properly. So basically set the genny up with an
earth spike like a TT system, and tie one leg of its output to the
earth."

Well, that turned out to apply in the case of my boiler, but why? Can
you explain it slowly and simply? Why does the flame sensing need this?

Bill


Dunno exactly - it's something to do with flame ionisation rectifying
the signal or something.

Also, as far as I can see on my 2 boilers, the return path for the spark
is via the casing, so if this isn't connected to one side of the supply
- preferably the neutral(!) - there's no conductivity. Similar, I
suppose, to a car engine - where the engine casting needs to be
connected to the -ve side of the battery for the spark plugs (and other
electrics) to work.


I can confirm this having had to reverse engineer the Potterton Netaheat
board to fault find. Feeds live through .001uf capacitor and 1M
resistor into the flame and looks for a DC component. Presumably would
not work if L & N were reversed at the supply.

Chris K