On Thursday, October 24, 2013 7:35:28 AM UTC+1, Tim Watts wrote:
I would advise not putting all the larger RCBOs (32A rings, heaters) next to
each other - apparantly localised heat build up is a problem. I left a 1
module gap every 2-3 on mine and the middle RCBO is a low current one
(lights).


I asked MK about this long ago, after he wibbled for a bit, I pointed out diversity must surely apply in domestic installs.

GCH fails:
- 14+ RCBO in a row, 11x 32A with 3x 6A at the end.
- Even if #2 & #3 are feeding 32A continuous you only have 16A left on an 80A fuse.
- RCBO heating is thus localised with nearby breakers running cooler.

E7 NSH is the heaviest domestic load:
- NSH are a fixed heating load, so fuse rating is the limit.
- Even 80A is spread over 6x 16A RCBO, each feeding a 13A 3.4kW NSH.
- RCBO heating above IIRC 40oC will reduce their actual trip rating, but not below 13A in 7hrs.

For domestic it should be quite ok, even on a 100A supply.

Whereas multiple 50A RCBO instant water heaters in a commercial environment may create a problem whereby the ambient is higher (nearby DIN transformer, timer motor) and the RCBO do not get time to cool down due to duty cycle.