Garage socket & pattress question and 17th Edition wiring regs
On 18/02/2013 21:21, John Rumm wrote:
On 18/02/2013 21:14, John Rumm wrote:
Some will argue that you can get even more load on it since a 13A BS1361
fuse
Sorry typo, BS1362 - 1361 are mains incomer fuses!
Incidentally. There has been a thought about ring mains that has
bothered me for some time.
in a perfect world, you have a continuous live loop and a continuous
neutral loop on a 32A MCB ring main, from teh CU to all the sockets and
then back to the CU.
What if you had a break in the cable between the CU and the last socket?
This converts the ring main to a radial circuit.
Lets assume the ring main is then loaded to its full capacity of 32A.
This would mean that *ALL* the current would be flowing along one route
between the CU and the first socket (assuming multiple appliances
plugged in a various points around the radial.
Can a single 2.5mm2 T&E really sustain a 32A continuous load?
Also as I understand it, you should only have a 20A mcb on a radial
circuit wired in 2.5mm T&E. if you complete the radial into a ring, then
the MCB can be changed to a 32A MCB.
|