bud-- wrote:


Perhaps this will explain:

"You've probably seen project requirements that call for the
grounding of piping systems and exposed structural steel. Those
requirements, although well intended, miss the mark. The stated
intention of such requirements is nearly always the removal of
dangerous voltage on specific types of metal parts in the event of a
ground fault. These metal parts include exposed structural steel
members, electrically conductive metal water piping systems, metal
sprinkler piping, metal gas piping, and other metal piping systems.
But these requirements fail to make that intention a reality. That's
because you remove dangerous voltage on metal parts through bonding,
not through grounding."


No source.


Sorry. I thought the material was righteous on its face. Evidently not. See:

"Grounding vs. Bonding - Part 10 of 12"
http://ecmweb.com/bonding-amp-ground...ing-part-10-12





The NEC has 3 electrodes that are *required* to be used as earthing
electrodes (where present).
One is metal water service pipe (10 ft...).
Another, in general, is structural steel (because of its connection
into the rebar systems in the concrete foundation).

Your source is incorrect - water pipe and structural steel *must* (in
general) be used as earthing electrodes.

If they are connected as earthing electrodes they are also "bonded".


"Your source is incorrect..."

Giggle




and

"The NEC (section 250-81 through 250-83) requires that the
electrical system connected to all of the following, if available
for grounding purposes: * metal frame of building
* concrete encased electrode (rod, pipe, plate, braided wire)
* ground ring and
* metallic water pipe with 10 lineal feet in contact with earth


The correct list has electodes that may already be present in a
building and does not include ground rings and everything after
"concrete encased electrode".


The NEC has noted that metal piping will corrode over time and
possibly lose its continuity with the soil (i.e. ground) or be
replaced by plastic pipe. Accordingly, should this occur, the NEC
has mandated the 3 other paths to ground be utilized."


Cite for corrode.
Cite where water pipe has worse corrosion problems that ground rods.


Does not exactly satisfy your request, but of interest:
"The NEC has noted that metal piping will corrode over time and possibly
lose its continuity with the soil (i.e. ground) or be replaced by plastic
pipe. Accordingly, should this occur, the NEC has mandated the 3 other paths
to ground be utilized."
http://www.ct.gov/dph/lib/dph/enviro..._Necessity.pdf


The NEC has NOT mandated that "3 other paths" to earth be utilized.


Yes it has. (See above)



In other words, attaching a metal water pipe to an earth ground is
used to protect the user from the plumbing, not to provide a ground
for the electrical system. Using metal water pipe as an electrical
ground is insufficient.


The requirement to use water pipes as an earthing electrode is in a
section on the earthing system and the electrodes to be used.
It is in your list of required earthing electrodes, above.

You have bullsiht information and are using a bullsiht source.

(What a surprise.)


I assume your "non-bull****" source is your own dim remembrance of things
past.