View Single Post
  #30   Report Post  
Posted to uk.d-i-y
harry harry is offline
external usenet poster
 
Posts: 9,188
Default One for the electrical boys, please ...

On Apr 13, 7:59*pm, "ARWadsworth"
wrote:
harry wrote:
On Apr 13, 7:37 pm, "ARWadsworth"
wrote:
Arfa Daily wrote:
We are in the process of taking some modern commercial premises, in
which the landlord is dividing down a 2k sq ft unit into two 1k sq
ft units, one of which will be ours. The electrical supply comes
into the unit that will not be ours, so the landlord is putting a
new supply into our bit for us as part of the deal. The currently
installed supply is three phase, with each phase company-fused at
100A, as far as I can see. We have approached NPower for a meter,
and one of the questions on the application form refers to the type
of meter required. The two three phase options given are "Three
Phase Whole Current" and "Three Phase CT".
I have not the slightest idea what the difference between these is,
or which it will be that we need ?? I have checked with the landlord
to make sure that it is a three phase supply that he is bringing
over to our unit, and he says that we will "need a three phase
meter for a 40kVA supply" First question then. If each phase is
currently fused at 100A, does that mean that the incoming supply is
25kVA per phase i.e. 75kVA, and that by dividing it between the two
newly created premises, that is how he arrives at 40kVA ?
Our demand will be fairly high. There will be two electrical fryers,
each loading at 2 x 9kW, so I guess if they are all on and heating
up together, that would be a demand of 36kW. There is also a ceiling
mounted airco / heater unit that I don't know the specs for . It's
not very big - maybe 2 ft square. Other than that, the demand will
be moderately low - some fume extraction which is only a few amps, a
couple of small fridges and freezers, lights (not more than 1kW) and
small odds and sods for a normal ring main. So, given the
*potential* for everything being on together, does that mean that
the supply he is proposing giving us, is going to be adequate for
our needs ?


Another question on the form is "Voltage - please delete" The three
options given are 415V 11kV and 33kV. I assume that the correct
answer there is 415V as it's a three phase supply direct into the
premises ?


Have you got 3 phase appliances? It is worth noting that 3x100A
fuses on a 3 phase supply does not give you 300A of available power
for 230V appliances (no matter how well you share the load between
the fuses) as the neutral is only rated at 100A.


I have not done 3 phase for a while (other than just connect up a few
machines) but 40kVA sounds like he has just multiplied 400 (the
nominal voltage between phases) by the 100A fuse. ISTR that it
should be multiplied by sq rt of 3 to get the maximum power.


With a bit of (bad) luck Dennis should be along shortly to explain
everything as he is a f***ing know all.


--
Cheers
Adam- Hide quoted text -


- Show quoted text -


If each phase was taking 100Amps there would be no neutral current at
all.
A neutral current only appears when the phase currents are unbalanced.


Not if the OP is only using 230V appliances.

Please pay attention to what is written.

--
Adam- Hide quoted text -

- Show quoted text -


It matters not If all were using the same Kw, Where the separate
neutral wires meet, the sum is zero.