View Single Post
  #6   Report Post  
Posted to uk.d-i-y
harry harry is offline
external usenet poster
 
Posts: 9,188
Default One for the electrical boys, please ...

On Apr 13, 7:37*pm, "ARWadsworth"
wrote:
Arfa Daily wrote:
We are in the process of taking some modern commercial premises, in
which the landlord is dividing down a 2k sq ft unit into two 1k sq ft
units, one of which will be ours. The electrical supply comes into
the unit that will not be ours, so the landlord is putting a new
supply into our bit for us as part of the deal. The currently
installed supply is three phase, with each phase company-fused at
100A, as far as I can see. We have approached NPower for a meter, and
one of the questions on the application form refers to the type of
meter required. The two three phase options given are "Three Phase
Whole Current" and "Three Phase CT".
I have not the slightest idea what the difference between these is,
or which it will be that we need ?? *I have checked with the landlord
to make sure that it is a three phase supply that he is bringing over
to our unit, and he says that we will "need a three phase meter for a
40kVA supply" First question then. If each phase is currently fused
at 100A, does that mean that the incoming supply is 25kVA per phase
i.e. 75kVA, and that by dividing it between the two newly created
premises, that is how he arrives at 40kVA ?
Our demand will be fairly high. There will be two electrical fryers,
each loading at 2 x 9kW, so I guess if they are all on and heating up
together, that would be a demand of 36kW. There is also a ceiling
mounted airco / heater unit that I don't know the specs for . It's
not very big - maybe 2 ft square. Other than that, the demand will be
moderately low - some fume extraction which is only a few amps, a
couple of small fridges and freezers, lights (not more than 1kW) and
small odds and sods for a normal ring main. So, given the *potential*
for everything being on together, does that mean that the supply he
is proposing giving us, is going to be adequate for our needs ?


Another question on the form is "Voltage - please delete" The three
options given are 415V 11kV and 33kV. I assume that the correct
answer there is 415V as it's a three phase supply direct into the
premises ?


Have you got 3 phase appliances? It is worth noting that 3x100A fuses on a 3
phase supply does not give you 300A of available power for 230V appliances
(no matter how well you share the load between the fuses) as the neutral is
only rated at 100A.

I have not done 3 phase for a while (other than just connect up a few
machines) but 40kVA sounds like he has just multiplied 400 (the nominal
voltage between phases) by the 100A fuse. ISTR that it should be multiplied
by sq rt of 3 to get the maximum power.

With a bit of (bad) luck Dennis should be along shortly to explain
everything as he is a f***ing know all.

--
Cheers
Adam- Hide quoted text -

- Show quoted text -


If each phase was taking 100Amps there would be no neutral current at
all.
A neutral current only appears when the phase currents are unbalanced.