On Jan 14, 5:55*pm, (A.Lee) wrote:
I've done a bit of testing this afternoon, and found a fault on a ring
main.
Continuity results:
E-E *0.40 ohms
N-N *0.19 ohms
L-L * *37 ohms * - *clearly a fault here.

I checked the 4 sockets on the ring for loose connections, and found no
apparent fault.
So next I joined up opposite ends of L+E, and measured R1 + R2 at the
sockets: *0.42 ohms, 0.42, 0.48, and 0.51ohms.

Clearly the resistance goes up as the sockets get further away.

Muddled thinking got me nowhere.
After a while, I was thinking that the cable must be damaged between the
final socket and the return cable.
But, a resistance of 37 ohms? That doesnt seem to be enough to be a
damaged cable.
(Insulation resistance was checked, and all fine at 1k M ohms)

Any thoughts?
Ta
Alan.

--
To reply by e-mail, change the ' + ' to 'plus'.


99% of faults are behind/on a socket. Are you sure you've found them
all. Have you removed the socket to test the cable, could be a faulty
socket switch?