View Single Post
  #25   Report Post  
Posted to alt.home.repair
Pete C. Pete C. is offline
external usenet poster
 
Posts: 6,746
Default Burnt electrical outlet and plug


wrote:


Good possibility? It is a definite FACT. With the 30 amp rating of the
conditioner,a 20 amp plug would be a requirement. Particularly on a 20
amp circuit.


Don't assume a 30A rating requires a 30A plug. That rating is the
maximum input current, and you can absolutely change the plug to a lower
rating if the load on the conditioner is less than full load. The
circuit protection is at the panel feeding the receptacle, so if that
receptacle is on a 15A or 20A circuit it is fine. If the load is too
high the breaker will trip.