On Mon, 06 Dec 2010 23:02:40 -0500, Bill wrote:

Scott Lurndal wrote:
writes:

To avoid "cycling the breakers", Lew advised running 12-3 from two 20
Amp breakers (it would not have occurred to me to do that).


I'm not sure what this means, but if you're running two 120v circuits
using 12-3 from a pair of 20A breakers, make sure the breaker handles
are tied together such that both trip if either one trips.

scott


Because???


Because 1) - it is code.
2) if one circuit trips and you assume the wire is "dead" you
could be - the black could be dead, and the red live, and a lifted
neutral (which is common to both) would be LIVE.