"Andy Hall" wrote in message
news
On Sun, 26 Oct 2003 17:57:04 -0000, "IMM" wrote:



1.
Assume a Keston Celsius with load compensation control. When the flow

and
return temps become closer together the system assumes the house is

nearing,
or up to, temp. It then modulates the burner down. When the return and

flow
temps become wiser the assumption is that the house is becoming colder

and
winds the flow temp up.

CH is only on the house warms up and the boiler drops the flow temp.

Fine.
The pool heater is switched in. The return temp from the pool is very

low
(17C) and this blends with the return of the house heating (say 30c) to

say
give a combined return temp of 21C. Great for boiler efficiencies. Less
gas is being used. The control system thinks the house is cooling and
ramps up the flow temp to max. Fine, as the pool heater needs this heat.
This means the flow to the house is too high. This is fine as TRV rad
valves will compensate for any heat gain; assuming they are fitted in the
rooms.

2.
The Keston boilers quoted are small commercial jobs with no modulation.


I think that you are thinking of the older models.


I am and I liked them a lot. I loved their simplicity.

These two
modulate from 11 to 40 kW and 14 to 55kW respectively.
The rig for them has the option of fully proportional controllers with
weather compensation and remote access and monitoring.


Sounds good I'll have to check them out.




---
--