On Mar 5, 11:45*am, John Rumm wrote:
NT wrote:
On Mar 5, 10:47 am, andrew wrote:
One of the legacy sites I still do a bit of maintenance on has a large
sealed thermal store with plate heat exchangers for DHW plus an underfloor
loop. It is normally solar powered with a wood burner for high demand.


It has a 3ph delta wired immersion heater provided as back up but, due to
cock ups in communication there is only a single phase supply.


Obvious solution is to pull the 3ph immersion out and replace with 240V one
but nothing has been done about this in 4 years. Spare parts for the wood
boiler take about 3 days to source and fit so there is a need for a back
up.


I talked with the electrician and pointed out one could supply 240V across
two of the immersion terminals and neutral on the third, which would drive
~0.6 of the current and produce 1/3 of the heat of each element in the
immersion. So the 9kW 3phase immersion would derate to 2 elements at 1kW
each, still better than nothing if the 240V supply is up to it. The
suggestion was immediately condemned as unsafe and inappropriate.


I can see that it would be in defensible as it is using equipment in a way
for which it isn't designed but unsafe? After all it's using 0.6 the
voltage and current it was designed for.


AJH


Surely you could get 2/3 the power into it by connecting the 3
terminals to L,L,N or N,L,L.


You would also be reducing the effective voltage, i.e. 240V L to N,
rather than 415V L1 to L2 etc.


yes...


Certainly nothing unsafe about it, as long as the single phase supply
is all upto it. Clearly not inappropriate either - but when people
react like that, any attempt at sense is futile.


Too true!


Don't overlook other space heat sources as well. Eg a hob can heat a
small or small-medium house temporarily.