wiring code ? for a detached garage
On 2009-11-10, jamesgangnc wrote:
Your list of items basically captures what I have but there is also
house fixtures on the same switches.
That's fine, it doesn't change anything I said.
I still need to install ground rods at the garage. It's 2 now isn't
it?
You need a grounding electrode system, which consists of
interconnecting _all_ the electrodes present. Then if there aren't
enough present, you need to add more. See NEC article 250 part III,
starting at 250.50.
Common electrodes a qualifying rebar or a 20' length of bare #4
copper wire in the footer of a foundation (required for new
construction, otherwise only if accessible), any metallic water pipe
that is buried for at least 10', and ground rods. The first one
(called a concrete encased electrode, or CEE) is deemed adequate by
itself; the other two are not adequate by themselves are require a
second electrode (which could be a ground rod).
Hope this helps.
Cheers, Wayne
|