Thread
:
Load capacity of 200-amp panel
View Single Post
#
35
Posted to alt.home.repair
propman[_6_]
external usenet poster
Posts: 22
Load capacity of 200-amp panel
Doug Miller wrote:
In article ,
wrote:
Consider this simple circuit analogy which is exactly what you would
have with a balanced load on a 240V service. It's a 240V voltage
source powering two 120ohm resistors.
____________ 240V___________
I I
I I
I I
---------120ohm---------120ohm---------
a b c
There is only 1 amp of actual current flowing in the circuit. Across
each resistor there is 120Volts and 1 amp of current flowing. So,
yes you have 1 amp flowing in EACH load, it is supporting two 1 amp
loads, but it's the same physical current flowing through each load.
The "service" is only supplying 1 amp of actual current, not 2.
What voltage do you measure between a and b? Between c and b?
What current do you measure between a and b? Between c and b?
That's what I meant when I said a 200 amp service cannot supply 400
amps of current.
But it can. 200A at 120V on each leg is a total of 400A at 120V. The two legs
of a residential electrical service are, in effect, two parallel circuits.
.....with a common neutral wire which must provide a return path for both
circuits.
200A flowing in each of two parallel circuits is 400A total, not 200A.
As long as the neutral wire is rated for an amperage capacity of
400A...if it's not, and you try feeding 400 amps through a wire only
rated for 200A max, what do you think will happen? ;-)
Reply With Quote
propman[_6_]
View Public Profile
Find all posts by propman[_6_]