View Single Post
  #8   Report Post  
Posted to alt.home.repair
Ed Sievers Ed Sievers is offline
external usenet poster
 
Posts: 4
Default Furnaced controller problem

Many thanks, MLD and all those who responded. A neat guy who has "been
around the block more'n a few times" servicing HVAC in this area came out
today (he works for a fairly large firm that has been here for many, many
years). He told me that lightning "gets after" 2 things in furnaces (with a
fervor)....namely, controller boards and gas valves!.....And many times,
both simultaneously. We have lots of lightning storms here in North TX, so
he sees this all the time. Within minutes, he disconnected the gas valve,
jumpered red and white on the stat connections and voila....the induced
draft motor started right up and shortly after, the igniter glowed brightly
...... following the logic of the new control board I had installed. His
company had to order the valve so it won't be in 'til Mon or Tues and I am
gonna just let him go ahead and install it. I asked him about a general
purpose gas valve (like I would buy on the cheap from Johnstone or another
HVAC supplier in the area) and he didn't recommend it ...... felt it should
be matched up to the controller board ('course the kinda odd lookin' OEM
part is at least 3 times the price through the company he works for.) I
have no doubt that this is gonna solve the problem and with that said, my
"lesson learned" is that the quick and dirty test I did on the gas valve
"didn't cut it". I figured that the coil in the valve would either be
"open" from a lightening-induced overvoltage or it would be OK. I measured
about 400 ohms (don't really know what's normal) so I thought the valve was
probably OK....but it isn't. After-the-fact, I believe that even though the
VOM measured 400 ohms, the actual impedance is probably another number
altogether......and it almost certainly "ain't good"....and the controller
didn't like it and wouldn't "proceed" either. Just pickin' this
knowledgeable/experienced guy's brain was worth half the outrageous price
his employer charges. 'Course I have heard that one of the "certain
characteristics" of old codgers like me is that "everything costs too much"
:-) but WOW $90 service calls + trip charges (only once no matter how many
trips are req'd....they are all heart) etc, etc. The grand total for all
this is gonna be close to 500 smackers with the tax! Yup, I was born (and
got into and out of the AC business) 30 years too soon.....at least.
Cheers, y'all Ed S. ps If there is a sequel to this tale.....I will
certainly share it with you, knowing it all adds to the ol' data
base...............and thanks again.
"MLD" wrote in message
...

"Ed Sievers" wrote in message
...
My daughter's furnace (and her little Boze radio) received a bit of a
jolt from a secondary leg of a lightning strike which hit (and
penetrated) the roof across the street this past summer. I had to
replace the furnace control board ($132 wholesale from an AC parts house)
and then the AC worked just fine the rest of the summer. I didn't c/o
the heater at the time, but she tried it the other day and it doesn't
work. I was very careful ground myself while installing the replacement
controller last summer so as to avoid static discharge and of course
labeled all the wiring to ensure I connected it up right. Now, on
startup, the induced draft fan starts a couple of times and on the 3rd
try or so, gets up enuff speed to trip the draft sensor switch and keep
running. The hot-surface ignitor never heats up though nor does the gas
valve open. Without a normal startup, eventually everything shuts
down...as it should. I thought maybe another lightning strike near the
house had "zapped" another controller, so I bought a replacement + a
spare. I have tried both the new ones......same result. All the flame
roll-out sensors, hi-temp sensors, etc are "made" and the gas valve reads
about 150 ohms, so I believe it to be OK. As a last resort, I
disconnected all the T'stat wiring (as per directions) and ran a "self
check" on the currently installed controller. After an intitial delay,
it is supposed to turn on the draft blower and leave it on, then the
ignitor (for 15 seconds .... but not the gas valve) , then turn on the
big blower at low speed (heat) for abt 30 sec and then high speed (cool).
Instead, I just get a flashing red status indicator light on the control
board......and the literature says this can either be: (1.) a problem
with the 120 v. power polarity (reversed) or (2.) a twining problem.
Well, the power is hooked blk to blk and white to white (as it has been
for 6 years now) so that isn't the problem but what the heck is a
"twining problem? Also, since the first event is supposed to be the
induced draft fan coming on.......I'm wondering if it may have some
lightning-caused shorted turns or something. I would think that the
control board only provides power to that little motor via a relay, but
maybe the board gets feedback info and is "smart" enough to know that the
current draw to that little motor ain't right? (That's a stretch, but I
am about at my wits end......and I intend to call out a tech who is more
up-to-date than I am on HVAC) Any thoughts from any AC wizards out
there? TIA.....ed s (long,long ago retired A/C dude) in TX.




From all that you've done I would suspect your igniter. You should be
able to see it glow if it's OK--no fire since you indicate that your gas
valve didn't open. As noted in another post, get it fixed and chalk it up
to the lightning strike--your insurance should cover the cost. On your
bill have it noted that failure was due to lighting.
MLD