View Single Post
  #28   Report Post  
Posted to alt.home.repair
Observer Observer is offline
external usenet poster
 
Posts: 16
Default Circuit breakers and breaker box

On Wed, 22 Jul 2009 11:47:51 -0400, wrote:

On Wed, 22 Jul 2009 09:14:25 -0500, Observer wrote:

Just curious, would it have been a big deal if they didn't install
this screw per code? I mean would it have made the panel not to code
just because of a neglected screw?



Yes

408.36(D) Back-Fed Devices. Plug-in-type overcurrent protection
devices or plug-in type main lug assemblies that are backfed and used
to terminate field-installed ungrounded supply conductors shall be
secured in place by an additional fastener that requires other than a
pull to release the device from the mounting means on the panel.



When I look back, your past posts all said the same thing and thank
you for the info. I guess this panel now is all up to code and all is
working fine as of this morning. Thank you a lot.